1 members (gfretwell),
47
18
Re. luckyshadow's comments: "Whats up with all those tie wraps ? I dislike seeing tie wraps in a panel - for 1 reason - HEAT !"
If the conductors are rated to handle the heat in conduit, I see no reason to worry about them getting heated in the panel due to being clustered under tie raps. Putting three phases and neutral in a tie wrapped grouping serves to minimize magnetic fields (per 300.20(A)) and helps to secure conductors in place.
Posts: 10,051 Likes: 39
"If the conductors are rated to handle the heat in conduit, I see no reason to worry about them getting heated in the panel due to being clustered under tie raps"
The exact same rule applies. If more than 3 are bundled more than 2 feet derating kicks in.
This subject sure has drifted, but since it has I would like to comment that I don't think the derating rules in 310.15(B)(2) apply to the gutter space in panels. I'm sorry, but I don't believe the intent was to apply these rules to panels because if we do most panels out there would not pass inspection. we would be derating every conductor in the panel. Now someone explain to this group what maintaining spacing is all about.
George Little
Hi, I wanted to reply to the original comment.
It has always been my understanding that the LINE SIDE should ALWAYS be at the TOP.
I thought this was standard practice where possible? I think this carries over from the wiring arrangement in disconnects.
A feeder can enter the enclosure at any accessible place within the enclosure but should still terminate at the top. I do not think that having the line side at the bottom is good practice.
I am talking about disconnects and panelboards not switchboards, mcc or switchgear.
I know electricians that even use the top screw on switches and outlets to terminate the line.
As far as I know there is no rule that requires this but it is done. It makes practical sense and logical sense.
A GFI is usually configured the same way. Line at top load at bottom.
It seems to me there is a rule somewhere that requires the line to be at the top? Maybe I am thinking of a spec.
It may be a good idea if you want to meet the american disabilities act by that I mean having the breaker at a lower position so that a person in a wheelchair could operate the breaker.
I was on a job where some hand cut some 350 MCM feeders to the load side of a disconnect because he did not know what he was doing. If he had experience and training he would have drifted to the top anyway!
I am a top breaker guy I guess.
The photos are interesting.
Regards
Greg
[This message has been edited by mustangelectric (edited 02-03-2005).]
A GFI is usually configured the same way. Line at top load at bottom What about when someone installs them with the grounding hole down?
Thats how we do it up in the woods!
Hi, Frank, that does not change the way the receptacle is CONFIGURED only its ORIENTATION.
I am talking about wiring or termination practices.
Good point though.
Regards
Greg
Hi, I looked at a 200A Sq-D panel yesterday before I installed it and the panel can be installed in any vertical position. I have always been aware of the LINE/LINE markings in the panel and knew that the panel could be installed breaker up or down.
I guess I have never really had a reason to do it.
I think it is better up high. People like to lay tools, parts and other FOD in the bottom of the panel. Having the breaker low could be inviting trouble.
Regards
Greg
My experience has included a number of times that moisture was coming into the panel's cabinet by way of the service entry cable or conduit. By running the service entry conductors into the bottom of the cabinet I limit the damage that such water will do to rust in the bottom of the cabinet rather than corrosion of the panel parts.
Locally most of the panels are installed in basements so using the bottom of the cabinet for service entry conductors leaves the top of the cabinet and the wiring troughs free for branch circuit and feeder conductors. -- Tom H
Tom Horne
