0 members (), 477 guests, and 10 robots.
#91238 01/06/05 07:21 AM
If a hot tub is installed on a screened porch of a dwelling and fed with a 50 amp GFCI protected circuit, is a disconnect required near the hot tub?
The 50 amp GFCI breaker isn't within sight of the tub.
shortcircuit
Workgear for Electricians
#91239 01/06/05 08:29 AM
Yes disco is needed. 680.12
#91240 01/06/05 09:41 AM
Thanx Electricmanscott...wish they would put that requirement in part 4 also to clear up the confusion that I get from the emergency shutoff rule(680.41)
shortcircuit
#91241 01/06/05 11:19 PM
The emergency disconnect is not required at single family dwellings.
#91242 01/06/05 11:38 PM
Jim, you're correct that the emergency disco is not required for single family dwellings however the SERVICE disconnect is still required to be within sight just like any other piece of equipment.
#91243 01/10/05 10:46 PM
What if there is circuit breakers or switches under the skirt that will disconnect the motor. Do they count?
#91244 01/11/05 12:16 AM
Yes, the disconnect(s) under the skirt of the spa or hot tub qualify as the required disconnect(s). They/it certainly would be within sight of the equipment served. Some have said that an additional disconnect is needed within sight of the spa or hot tub. The '02 code seems to make it a lot clearer to me by saying "within sight of it's equipment" 680.12 and not "within sight from all pools, spas, and hot tub equipment and shall be located 5' from the inside of the pool, spa, or hot tub" as it did in the '99
George Little
#91245 01/11/05 06:52 AM
George, I think that the disconnect required by 680.12 should be seperate from the tub altogether.What if the hot tub is defective and they want to remove it and replace it with a new one?
shortcircuit
#91246 01/11/05 08:09 PM
680.12 says the disconnecting means shall be
accessible & within sight from its equipment
look at the definition of accessible, I do
not think the disconnect under the spa meets
that requirement.
#91247 01/12/05 12:19 AM
Wait a minute here- Are we trying to say that the disconnect under the skirt of a spa is not "accessible and within sight of it's equipment" 680.12? I would think that if I'm working on the equipment associated with the disconnect, that I would have the spa/hot tub opened up and this would provides accessibility and within sight. The relationship is between the disconnect and the equipment. You want to install an additional disconnect within sight of the spa/hot tub? Go for it. I'd like to bid against you.
George Little