Okay here's my understanding of the following:
(Quote)Could you then comment on 310.15(4)(a) and also 310.15 (4) (c)
An electricians call? an engineers call? (Unquote)

(a) is talking about a Delta system where the common (neutral) conductor only carries the unbalance current between the two phase conductors and the two phase conductors are 180 degrees out of phase with each other so there could be and probably is some cancellation taking place thus reducing the current flow in the common conductor.

(b) is talking about a Wye system where the two phase conductors are only 120 degrees out of phase so we don't have the same amount of cancellation as we had with the Delta system. Code panel says we need to count this as a current carring conductor.

(c) is talking again about the Wye and addressing not only the phase issue but the harmonics issue due to the non linear load placing extra duty on the conductor.

As to who's call this is? Everyone's.


George Little
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Sep 2003
Posts: 650
W
Member
The inspectors approach would be entirely appropriate if all of the conductors were bundled together in one place. If, working table 310.16 and the derating rules and the like you get something different, I posit that this is simply an artifact of the way 310.16 simplifies a complex situation.

The ampacity as determined by 310.16 is not an absolute number set by physical law; it is an approximate number set by making conservative estimates of things like thermal insulation and air flow and all the various factors which influence ampacity. I presume that this is the reason for the 'under engineering supervision' note.

The ampacity of a conductor is set by several factors; the heat generated by the conductor, the thermal compatibility of the insulation system, the heat carried away by the surroundings, and any other heat being produced in the surroundings.

If you run copper at the same current density (same amps per circular mil), then you will get the same heat production per unit of copper. Doesn't matter if you put 230A in a #4/0 or 115A in each of two #0 conductors; for the same length you will produce the same total heat. Bundle the two #0s together and the factors affecting ampacity will be the same as the #4/0.

It is only because the #0 conductors can be spaced apart than the total ampacity of 2 #0 conductors is greater than that of a single #4/0; you can get better heat dissipation.

-Jon

Joined: Dec 2000
Posts: 15
P
pip Offline OP
Member
All the conductors were running through a 12" nipple, so derating was not a factor.315(b)(2)(a). This inspector got mad at my written response and sent back a note "refer to 90.4".(authority having jurisdiction bla bla blaaa).....that was pretty weak if you ask me.

He also wanted me to supply my ground rod with a 1/0 thhn. I had already brought a 1/0 to building steel. I quoted 250.53(E) (supplemental grounding electrodeshall not be required to be larger than #6 copper).
He didn't like that one much either.

All said and done there is a piece of 1/0 going to the ground rod and i added (1) more set of 3/0 thhn to make him happy about the whole cir mil idea. Had to change all my lugs to make that one work [Linked Image]. What can you do? Thanks again for all your help.

Joined: Jul 2004
Posts: 10,054
Likes: 40
G
Member
"If you run copper at the same current density (same amps per circular mil), then you will get the same heat production per unit of copper."
When you parallel those conductors you end up with a lot more surface area to dissipate that heat and you increase the skin effect.


Greg Fretwell
Joined: Mar 2003
Posts: 48
G
GTE Offline
Member
PIP,
I think the inspector is confusing this with the requirements of the International Residenial Code, Table E3503.1