Hi, Is there ANY requirement in the NEC that requires a switch or disconnect to be Service Entrance rated?
Please quote the article if known.
Thanks for any replies.
-regards
Mustang
[This message has been edited by mustangelectric (edited 11-23-2004).]
|
|
|
|
|
Joined: Mar 2003
Posts: 21
Member
|
How about when it is used for SERVICE EQUIPMENT? I have always used a service equipment rated disconnect or enclosed breaker as the first throw on a service. Most discos that are not service equipment rated have no means of grounding the neutral.
|
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
2002 NEC See 230.66, 110.9 & 110.10
Joe Tedesco, NEC Consultant
|
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Try discussing this question with the utility company. I was unable to find the name of the local electrical inspector.
Electric Department Electric Utilities Manager Rex Garrett (479) 271-3135 rgarrett@bentonvillear.com
Electric Utilities Assistant Manager Paul Kellenbarger over Technical Design (479) 271-3159 pkellenbarger@bentonvillear.com
Electric Utilities Assistant Manager Donnie Johnson over Construction (479) 271-5985 djohnson@bentonvillear.com
Joe Tedesco, NEC Consultant
|
|
|
|
|
Joined: May 2004
Posts: 162
Member
|
you might consider the requiremnt in 225 regarding the marking of equipment, in addition to those references previously mentioned
225.36 Suitable for Service Equipment. The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
Charlie
[This message has been edited by cpal (edited 11-23-2004).]
|
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
Hi, Thanks for the replies. I should have said a SWITCH or DISCO used as the Main.
I appreciate the code references.
-regards
Mustang
[This message has been edited by mustangelectric (edited 11-23-2004).]
|
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
Hi, I think Art 110.9 and 110.10 cover this.
Thanks
Mustang
|
|
|
|
|
Joined: Mar 2001
Posts: 345
Member
|
225.31 Disconnecting Means. Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure. 225.36 Suitable for Service Equipment. The disconnecting means specified in 225.31 shall be suitable for use as service equipment. Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.
I would think that about covers it. -- Tom Horne
Tom Horne
"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
|
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
Hi, Yes that would cover it. Why are inspectors so adamate about getting the SE rating of a disco sold to the public?
IS there a big counterfit market? Don't manufacturers have to meet this when they design these devices?
The inspector I am dealing with sent a comment letter asking to verify compliance with 110.9 and 110.10.
Thanks for pointing those out and the great replies.
-regards
Mustang
|
|
|