0 members (), 175 guests, and 7 robots.
#90495 11/23/04 04:13 PM
Hi,
Is there ANY requirement in the NEC that requires a switch or disconnect to be Service Entrance rated?
Please quote the article if known.
Thanks for any replies.
-regards
Mustang
[This message has been edited by mustangelectric (edited 11-23-2004).]
Workgear for Electricians
#90496 11/23/04 04:39 PM
How about when it is used for SERVICE EQUIPMENT? I have always used a service equipment rated disconnect or enclosed breaker as the first throw on a service. Most discos that are not service equipment rated have no means of grounding the neutral.
#90497 11/23/04 04:40 PM
2002 NEC See 230.66, 110.9 & 110.10
#90498 11/23/04 05:05 PM
Try discussing this question with the utility company. I was unable to find the name of the local electrical inspector.
Electric Department
Electric Utilities Manager
Rex Garrett
(479) 271-3135
rgarrett@bentonvillear.com
Electric Utilities Assistant Manager
Paul Kellenbarger
over Technical Design
(479) 271-3159
pkellenbarger@bentonvillear.com
Donnie Johnson
over Construction
(479) 271-5985
djohnson@bentonvillear.com
#90499 11/23/04 05:47 PM
you might consider the requiremnt in 225 regarding the marking of equipment, in addition to those references previously mentioned
225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
Charlie
[This message has been edited by cpal (edited 11-23-2004).]
#90500 11/23/04 07:20 PM
Hi,
Thanks for the replies. I should have said a SWITCH or DISCO used as the Main.
I appreciate the code references.
-regards
Mustang
#90501 12/07/04 12:33 PM
Hi,
I think Art 110.9 and 110.10 cover this.
Thanks
Mustang
#90502 12/08/04 01:21 AM
225.31 Disconnecting Means.
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.
I would think that about covers it.
Tom Horne
Tom Horne
#90503 12/08/04 09:01 AM
Hi,
Yes that would cover it. Why are inspectors so adamate about getting the SE rating of a disco sold to the public?
IS there a big counterfit market? Don't manufacturers have to meet this when they design these devices?
The inspector I am dealing with sent a comment letter asking to verify compliance with 110.9 and 110.10.
Thanks for pointing those out and the great replies.
-regards
Mustang