Hi, Is connecting the gec to building steel on a commercial job accpetable versus cold water bond?
it seems to me that you need both but parallel paths could be an issue.
i am looking at a riser diagram that calls for 3 3/4"X8' ground rods placed 10 feet apart and instructions to connect to building steel where possible..
it seems to me that you need a building steel connection and you need a cold water bond..200A service requires a #6 AWG GEC to a made electrode..and a #4 AWG GEC to cold water..correct?
thanks
mustang
thanks for any replies.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
You must use all available electrodes. See 250.50
As far as the sizing goes, yes, you are correct.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Jun 2004
Posts: 220
Member
|
250-50 says if available bond every thing together. sizes look good. #4 also to the steel. Ryan you beat me [This message has been edited by trekkie76 (edited 10-12-2004).]
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
so you are saying that there SHOULD be a cold water bond IF AVAILABLE?
i am asking because i am working from a set of plans that just ask to bond to three 3/4 X 8' ground rods and to the building steel. the building has copper piping installed. i always bond the copper at the point of entry into the building or first accessible loc
should i make a revision on the dwgs and call for a COLD WATER BOND using a #4 AWG? and should I revise the dwgs to call for a #4 AWG to the ground rods and the building steel? I though #6 was good for MADE ELECTRODES?
sorry if this is elementary to you...grounding is the most important part of any electrical system and it is one of the FUZZIEST too!
i am big on grounding!
thanks
mustang
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
This may help The engineer is free to ask for more than code minimums. The Power company around here asks for 4/0 to 3/4" 10' ground rods at transformer pads. The NEC would say 6 AWG would be enough. Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Yes, if it is there and meets the description of an electrode, you must bond it with (in your case) a #4.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
yes that slide clearly shows the best means to accomplish a proper grounding system
That looks like the same slide on the first page of the NEC handbook
and thanks for the follow up comments regarding the #4
thank you very much!
mustang
[This message has been edited by mustangelectric (edited 10-13-2004).]
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
are the articles:
GEC:250.66 Bonding Jumper: 250.122
regards
mustang
[This message has been edited by mustangelectric (edited 10-13-2004).]
|
|
|
|
Joined: Aug 2003
Posts: 64
Member
|
are the articles: GEC:250.66 Bonding Jumper: 250.122 No, when we're talking about bonding jumpers within the grounding electrode system, they are also sized according to 250.66. (see 250.53(C))
|
|
|
|
Joined: Jun 2004
Posts: 220
Member
|
to the made electrodes does only have to be #6. I was talking about to the steel being #4
|
|
|