In some areas consider the water pipe is the primary ground, the rod is secondary. (Due to soil conditions) It's a bit of a throw back to the days before PVC was acceptable for wide use in many areas of the country. Also not too long ago, ANY cold water pipe ANYWHERE was considered an acceptable ground. (not any more...) Recentley, we changed (locally?)to bonding gas lines at the nearest point past the meter. Point is things and attitudes toward the concept change....
Recently, during lunch watched a CATV contractor get chewed out by his boss for grounding his installation to a rod or water, instead of the main panel itself. ?????? (Didn't want to butt-in....)
shortcircuit, I think a simple jumper to a water (grounded), or equipment ground would be fine. This is an alarm panel, not a Service.
250.20 (A) Alternating-Current Circuits of Less Than 50 Volts. Alternating-current circuits of less than 50 volts shall be grounded under any of the following conditions:
(1) Where supplied by transformers, if the transformer supply system exceeds 150 volts to ground
(2) Where supplied by transformers, if the transformer supply system is ungrounded
The branch circuit is grounded right?
Now what is a "ferrite bead", and what purpose does it serve?