tell me if i get this question right about the tap rules here the max length for the tap is 25 feet aka 8 meter length rules too.
but what happend if the tap do run at 33 feet [ 10 meter ] length then the rules do change too ??
I think you are swapping standard for metric measurements.
The lengths of taps that I know of are taps not over 3 m (10 ft) Long and taps not over 7.5 m (25 ft) Long.
i did see few tap do run more than 25 feet [7.5 meter]
If you did see a tap over 25' IMO it is not a tap, it is be a feeder and has to be protected at the supply end not at the load end of the conductors.
There are times outside for transformer secondary conductors you can tap longer than 25' feet. Service conductors come to mind.