#87616 03/26/04 07:02 PM
Joined: Mar 2004
Posts: 2
C
citysis Offline OP
Junior Member
I need clarification on code in NYC for gfci's.
In a residential kitchen, is the outlet within 3' of the sink 'required' to be gfci or 'recommended' to be gfci?

Work Gear for Electricians and the Trades

Workgear for Electricians

#87617 03/26/04 07:47 PM
Joined: Nov 2000
Posts: 2,148
R
Member
I don't know the NY code, but in the NEC all outlets that serve the kitchen countertops must be GFCI protected.
Don


Don(resqcapt19)
#87618 03/26/04 08:16 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
The NYC Electrical code has not modified the NEC-1999 Article 210-8.
All recepts that are installed to serve counter top surface require GFCI. There is no distance requirement.


Ron
#87619 03/27/04 08:12 AM
Joined: Mar 2004
Posts: 2
C
citysis Offline OP
Junior Member
I thought as much but wasn't sure that it wasn't ammended. thank you all very much for the info.

#87620 03/27/04 08:49 AM
Joined: Oct 2001
Posts: 597
E
Member
When was the outlet in question installed?

This is an important part of the formula that hasn't been stated. Left to the NEC, the only regulation that applies to a kitchen counter receptacle is that which is in effect at the time of installation.

Is the outlet in question existing, proposed, or newly installed?


Al Hildenbrand