given a GFPE, what if the circuit is 240 vac single phase (heat trace) WITH NO neutral?
if there is no neutral in the circuit these require a special breaker with NO neutral...
a GFPE breaker with a neutral requires a neutral in the circuit to work properly the way i understand it..
the breaker i have is a two pole cutler hammer with a neutral...the problem with the circuit i am working with is that there is no neutral so this type of breaker is not the correct type in my opinion...we have a lot of heat trace using these breakers but there is no neutrals in any of the circuits...
in my opinion this breaker will only work on overcurrent..with no neutral..
[This message has been edited by frodo (edited 12-03-2003).]
[This message has been edited by frodo (edited 12-03-2003).]
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Those breakers don't require a neutral on the load side to work correctly. They look at the current on the two hots and the neutral to see if these currents sum to ~0. Even if one of the 3 load conductors does not have current or is not connected, the current on the other two will still sum to ~0. When the current sum gets to 30mA, the breaker will open the circuit. Don
Don(resqcapt19)
|
|
|
|
Joined: May 2001
Posts: 129
OP
Member
|
hi, thanks for the reply. maybe my post wasn't so clear.
the circuit is only single phase 240...with NO NEUTRAL..
the breaker has an integral neutral but no INCOMING neutral...
i would agree with your post if the circuit in question contained a neutral...
thanks for the responses
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Does the panel where the breaker is installed have a neutral? Don
Don(resqcapt19)
|
|
|
|
Joined: May 2001
Posts: 129
OP
Member
|
hi, the panel itself has a neutral bus that is connected to the midpoint of the xfmr...
there are no incoming neutrals to the breakers themselves, but the integral neutral wire is connected to the N-bar..
i do not see how the breaker could work properly without the neutral in the circuit...i believe the wrong breakers were specified..
thanks for the help..
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
As long as the neutral pigtail on the breaker is connected to the neutral bus in the panel the breaker will work fine. There is no need for a neutral connection on the load side of the breaker as long as the load itself does not require a neutral. Don
Don(resqcapt19)
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
frodo,
If you still have the little 'instruction' sheet that came with this breaker take a look at it and see what it says. The last time I saw one it mentioned how to install with or without a Neutral.
If you do find something there please post the language here so we will have it available for others with the same question.
Bill
Bill
|
|
|
|
Joined: May 2001
Posts: 129
OP
Member
|
hi, thanks for all the replies...i spoke to cutler hammer and they said that the breaker will work without a neutral in the circuit...
the part number is:CUTLER-HAMMER QBGFEP 2020
i was not aware that this type breaker would work without a neutral in the circuit...
thanks again for the replies..
frodo
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Brendan Foley of Cutler-Hammer was kind enough to forward a page from their Catalog to me. The diagram below (extracted from page) is the same that is included in the Instruction Leaflet that ships with these breakers: Bill
Bill
|
|
|
HCE727
Delaware County, PA, USA
Posts: 187