ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photos of the Week:

Snakes!!
Snakes!!

Random Gallery Image:
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 615 guests, and 34 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#85256 06/13/03 07:22 PM
Joined: Jan 2003
Posts: 59
C
ccdave Offline OP
Member
with three options for grounding the unmetered leg of a 3 phase service, ground rod, cold water or building, which is the best and safest???????
thanks--dave

Horizontal Ad
#85257 06/13/03 09:26 PM
Joined: Oct 2000
Posts: 5,393
S
Member
the most local earth contact available would get my vote.....

#85258 06/13/03 11:08 PM
Joined: Nov 2000
Posts: 2,148
R
Member
You don't have a choice. If there is a metal underground water piping system, you must use it. If there is effectively grounded building steel you must use it. If they both exist, you must use them both. If you have only the water pipe, you must supplement it with a made electrode and comply with the 25 ohm rule in 250.56 for the made electrode.
Don


Don(resqcapt19)

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Popular Topics(Views)
363,808 Are you busy
286,713 Re: Forum
265,148 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5