If you made the neutral-ground bond at the meter, then it shouldn't be done at the panels too.


Ron
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Nov 2000
Posts: 2,148
R
Member
Ron,
If the panels are the service disconnects, 250.24(B) requires a bond in the panel even if there are other bonds on the line side of the disconnect(s).

gserve,
If there is not a factory provided method of bonding the grounded conductor to the enclosure, these panels are not listed for use as service equipment.

Don


[This message has been edited by resqcapt19 (edited 05-19-2003).]


Don(resqcapt19)
Joined: Mar 2003
Posts: 92
G
gserve Offline OP
Member
Don, These panels say on the label on the door to "ground" if required and have a arrow that points to the neutral bar. They are about 30 years old