I got a side job from one of the manangers at work. (not my dept) to hook up her hot tub.
The tub is located approx 40 ft from the house. It is a pretty big one with an gazebo type roof. It appears to be 120/240 or maybe just 240, the instructions are for about 6 different tubs. Nameplate states 50 amp max breaker, and theres a tag that says it MUST be GFCI protected. You should have seen the look on her face when I told her what a 50 amp gfci breaker cost. But so far all well and good.
First question is where do I put the disco if in fact I even need one? There is only two choices, on the house within sight, or on the tub itself (which I am not crazy about).
Second question is she stated she wanted a plug so she could plug in some christmas lights on a tree approx 5-6 feet from the tub. Can I install the plug, gfci protected of course, on the side of the tub with an in use cover? Or do I need to trench to the tree and mount it on the tree? Keep in mind the only other structure is the house 40 feet away.
Last is not a code question exactly but refers to "protection from physical damage" when running PVC pipe. It has been by experince that lawn mowers hunt down the pipes and break them on a regular basis. I was thinking of running a one size larger emt or rigid sleeve over the PVC where it comes out of the ground. Would that be acceptable? Are there any other tricks to trying to protect the pvc?
These may seem like a lot of questions for an experinced electrician. Since most of my experince is commerical I do have questions about resi stuff, keep in mind if this was a commerical hot tub it would be rigid all the way with stainless steel discos.
One other note, the customer lives in the sticks, really out in the sticks. The hot tub people will NOT hook it up, they gave her a list of some contractors to call, she called like 7 of them but none are intrested. Thats how I got involved.
|
|
|
|
|
Joined: Oct 2002
Posts: 210
Member
|
Outdoor hot tubs follow the same rules as wiring a swimming pool. Conduit has to be run back to the panel, a disconnect within sight at least 6ft away. GFCI protection and bonding as required.
She should use a licensed electrician and have it inspected by the AHJ.
|
|
|
|
|
Joined: Mar 2003
Posts: 97
OP
Member
|
I am licensed.
My understanding with the customer is there is not much if any AHJ where she lives. I belive she lives in an unincorperated area.
The reason I ask about the disco is the last sentence to section 680.41
I found one of those Hot Tub boxes which have the 50 Amp gfci breaker in them. So that solves this problem, funny thing is that I need to get another breaker to feed it from the panel.
It will be run it in conduit. Was just asking if anyone had any tricks to protect it from the lawn mower.
I got a total of $750 so far in material and labor and that includes the trencher rental. That sound about right to hook up a 50 amp hot tub? Its a 50 feet trench to the house with another 50 feet to the panel in the attic.
|
|
|
|
|
Joined: Oct 2000
Posts: 4,163 Likes: 6
Member
|
drillman,
The price sounds very reasonable and even a bit low to me. But aside from that, is the Tub there already? is it going to be on a platform, deck or concrete slab etc.? On some Tubs the conduit can even stub up directly into the area where the control panel is. That way you wouldn't have to worry about any Lawnmowers etc.
The Panel is in the Attic?
Bill
[This message has been edited by Bill Addiss (edited 04-27-2003).]
Bill
|
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
Why not use rigid to come out of the ground instead of trying to protect the PVC?
Curt Swartz
|
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Although 680.41 doesn't require an emergency switch, 680.12 requires a disconnecting means. The NEC dictates the MINIMUM requirements for electrical installations. Usually we can do better at little more cost. And you should have it inspected. BTW, I'm sure she wasn't stunned at the cost of the hot tub, why is she looking for a "deal" to have it installed. Remember, she probably earns (and I use the term loosely) several times what you do. If she doesn't want to pay you to do it right, let her take her chance with the Yellow Pages. (Do I sound bitter?) ![[Linked Image]](https://www.electrical-contractor.net/ubb/biggrin.gif) [This message has been edited by Redsy (edited 04-28-2003).]
|
|
|
|
|
Joined: Mar 2003
Posts: 97
OP
Member
|
The hot tub is already installed it is on some sort of brick pilings. I will stub up directly inside it therefore no problem with pipe damage.
The problem with pipe damage is on the wall of the house where the disco will be.
The panel is not in the attic, but it is inside about 30 feet away from where the tub is, hence the run in the attic after I get to the house. Would be nice if it was outside.
I am quite aware what she makes as a manager type person. As stated in my first post she lives in the sticks and cannot find a contractor to come out and even look at this.
More than likely I will use rigid from the disco down to the first 90 so it will not get broken.
Belive me, I wish there was an estimate from another contractor so I can compare. In the past when offered side work I have told people to get a legit estimate first and then see if I can even save them anything. Most of the time I cannot. In fact most side work I have done is on the barter system.
I will look into having it inspected.
Thanks for all your help
|
|
|
|
|
Joined: Jan 2003
Posts: 8
Junior Member
|
Disconnect needs to be at least 5 feet away and in sight. General outlet needs to be installed more then 10 feet. Less than 20 feet away. Pvc pipe needs to be 18 inches under ground. Some tubs require there own ground rod.
|
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Interesting suggestion regarding the ground rod. I've heard of inspectors requiring this, but there is no NEC issue and I can't understand what the purpose would be.
|
|
|
|
|
Joined: Mar 2003
Posts: 97
OP
Member
|
I did not get the job
she found a local guy to do it for half my price. He even has his own ditch witch so he will not need to rent it.
one of the pitfalls of doing side work.
Yes, I padded my bid a little. This being a connected person at my day job, I would have made sure she was happy, just was not going to lose my shirt on it.
Oh well alls well that ends well, I know more about hot tubs now.
Thanks for all your help guys.
|
|
|
Posts: 21
Joined: September 2019
|
|
|
|