Is it agianst NEC to use 15 amp snap switches for lights where the branch circiut is on a 20 amp breaker? I see this done all ther time and cant find an answer in the code book 2002.
I'm not sure myself, but general snap switches are rate either 15amp or 20amp right on the switch. Unless there is some code for switches comparable to 210.21 for receptacles, like maybe 210.23 it could be a toss up. I think I would allow it depending on the load.
Russ
[This message has been edited by russ m (edited 03-30-2003).]
2002 NEC 404.14 snap switches shall be used within their ratings.
If you look at the whole article, to me it seems they mean the load and not the circuit but I am not sure.
Posts: 7,413 Likes: 9
IMHO, the switch rating is related to the connected load that the switch controls. Also, a good designer takes into consideration what type of "load" the switch controls. IMO, the resi guys use the 15 amp switches almost 100%. Comm guys tend to use the 20 amp rated. I can't remember having a call-back for a bad switch, as we install the 20's most of the time. It's also a "spec" thing....if the prints/specs say "20 amp rated switches" then it's a no brainer. John
If your OCD is 20A, I would not create a week point with a 15A switch. If your load is such that 15A is sufficient, I would change the OCD to 15A and put a 15A switch in.
Posts: 4,161 Likes: 5
In my opinion the switch rating is related to the load as Bob (Iwire) and John (Hotline) had said. A typical Dimmer switch is rated at 600W and I've never seen a 5A circuit breaker.
Kale: Quickly, what I mean is 20 amp branch circuit Feeding lighting in 5 office rooms Each office has 2 fixtures @ 3 amps total Each Office gets a 15 amp switch (spec grade) (or 20 amp isf engineer/arch has spec) Load thru switch is 3 amps
20 amp branch circuit Feeding lighting in one room Lighting load is 15 amps Switch is 20 amp (spec grade)
In the first example, we could OCP the circuit at 15 amps; but we run all 20's in comm, unless spec says otherwise.
Posts: 1,498 Likes: 1
Bill brought up Dimmer switches:
At least the European dimmers are always fused. I expect the American to be too. Unfused dimmers are allowed, but the safety requirements (oversizing) for these are so severe that the manufacturers don't make any.
A light switch is a different matter, since it isn't fused. However, as long as it can cope with the load and the short circuit current, there isn't a safety issue. Look at the ordinary switches on lamp cords or in table lamps. They a rated for only a few amps, but you are allowed to plug them into an ordinary socket. The only risk - which I'm sure doesn't exist of you follow the NEC - is a short circuit which doesn't trip the breaker instantly.
This of course doesn't answer the question if it is legal.
I've never seen a dimmer switch that was fused (i'm assuming you mean either a fusable link on the wire, a resettable fuse on the device itself somehow, or well, i'm not sure), i just know that our dimmers in US & Canada have no overcurrent protection what so ever, if it's rated at 600watts and you pump 1000watts through it, it gets too hot and makes fire, or whatever else thats going to happen happens ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
Zack,
Yes, I meant a fuse in the the device. (Ranging from simple glass fuses, to self resetting overcurrent protection)
I'm surprised, considering the high level of electric safety otherwise aimed at by US and Canada. But, on the other hand, that ought to answer the original question: If it is legal to install a dimmer switch, a regular light switch must be legal too, right?