it has always been my impression that the "zone" over a tub measuring 8' from the lip of the tub up and 3' out needs to be a covered recesed can. but that isn't what the code says. any opinions?
410.4(D) will permit a surface mounted, or recessed fixtures in "the zone". Only cord connected, hanging, track, or pendant fixtures, and paddle fans are prohibited.
Spyder, A wall next to a tub is no more a wet location than a wall next to a sink. Falcon, you said correctly, that is not what the code says. Hey I want cool name too. Maybe I clould be Cheetah or something like that.