0 members (), 3,614 guests, and 9 robots.
#81731 09/13/02 09:24 PM
Eandrew Offline OP
Does a nipple need not be supported if it is equal to or less than 18 inches long? Any code references for this?
Workgear for Electricians
#81732 09/14/02 09:46 AM
I could be wrong, but I would see no need for support for any conduit less than 3' long...
No code references... Sorry...
-Virgil
5 Star Inspections
Member IAEI
#81733 09/14/02 11:04 AM
Sparky,
What about 344.30?
(A) Securely Fastened. RMC shall be securely fastened within 900 mm (3 ft) of each outlet box, junction box, device box, cabinet, conduit body, or other conduit termination. Fastening shall be permitted to be increased to a distance of 1.5 m (5 ft) where structural members do not readily permit fastening within 900 mm (3 ft). Where approved, conduit shall not be required to be securely fastened within 900 mm (3 ft) of the service head for above-the-roof termination of a mast.
This same wording is used in the other raceway Articles. I know that nipples are commonly installed without support, but I don't find any exceptions in the NEC to premit that practice.
Don