#81731 09/13/02 08:24 PM
Joined: May 2002
Posts: 68
E
Eandrew Offline OP
Member
Does a nipple need not be supported if it is equal to or less than 18 inches long? Any code references for this?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#81732 09/14/02 08:46 AM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
I could be wrong, but I would see no need for support for any conduit less than 3' long...

No code references... Sorry...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#81733 09/14/02 10:04 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Sparky,
What about 344.30?
Quote
(A) Securely Fastened. RMC shall be securely fastened within 900 mm (3 ft) of each outlet box, junction box, device box, cabinet, conduit body, or other conduit termination. Fastening shall be permitted to be increased to a distance of 1.5 m (5 ft) where structural members do not readily permit fastening within 900 mm (3 ft). Where approved, conduit shall not be required to be securely fastened within 900 mm (3 ft) of the service head for above-the-roof termination of a mast.
This same wording is used in the other raceway Articles. I know that nipples are commonly installed without support, but I don't find any exceptions in the NEC to premit that practice.
Don


Don(resqcapt19)

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
BigB 8
triple 3
Popular Topics(Views)
302,657 Are you busy
231,942 Re: Forum
216,602 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5