0 members (), 919 guests, and 8 robots.
#8118 03/08/02 12:36 PM
F
Our main building has a 120/208 Volt, 3Ph, 4W. electric service. We would like to install a panelboard in a remote building. It does not have any 3Ph. loads. According to the NEC must a 120/208 Volt, 3Ph, 4W. panelboard be installed in remote building or would a 120/208 Volt 1Ph. panel be compliant?
#8119 03/08/02 01:02 PM
Frank,
That is a design issue and not covered by the code. If you do this please remember that all neutral conductors will be current carrying for derating purposes.
#8120 03/08/02 02:06 PM
F
Thanks for reply Don. The only thing I found in the NEC that was even a little bit related, if at all was Article 210.11(B) "Load Evenly Proportioned Among Branch Circuits".