#77265 05/17/01 10:28 PM
sparky Offline OP
What, in your opinion, is the most overlooked code?
Work Gear for Electricians and the Trades
Workgear for Electricians
#77266 05/18/01 07:46 AM
IMHO, the one mostly ignored here is strapping of conduits by electricians. When it comes to John Q Public, it seems to be workspace.
#77267 05/18/01 09:54 AM
Close race between these here in WV:
1) Box fill
2) Conduit fill (NM Cable especially)
3) Derating of bundled conductors
4) Proper cover for buried pipe or cable
Sorry I didn't quote the good book, it's in the truck and I'm feeling lazy...
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#77268 05/18/01 04:11 PM
sparky Offline OP
nec's not needed, we know what you mean [Linked Image]
#77269 05/18/01 07:28 PM
Tom Offline
This is impossible to narrow down to one or two, but these make my list
Lack of wirenuts on equipment ground splices
Equipment grounds not connected to boxes
Multiple wires on/in a terminal
Box fill
Working space/clearance
Working space/clearance (keep repeating this about 100 times)
Oh, so that's what the green screw is for (as applied to panelboards)
Grounded conductors used for grounding conductors.
Tom
Few things are harder to put up with than the annoyance of a good example.
#77270 05/18/01 08:38 PM
doc Offline
Think this is the most overlooked of them all " a neat,safe and workman like manner" and one more is "panels and circuits not being makred properly"
MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE