0 members (), 194 guests, and 8 robots.
Page 3 of 3 1 2 3
#76191 02/04/01 04:55 PM
Very interesting thread here....a few years back "harmonics" was the buzz word in the trade, you could'nt swing a dead cat without hitting an article about it, fixtures & equipment started comming out with a THD rating. Courses started popping up , and of course, every trade mag followed suit...
Work Gear for Electricians and the Trades
Workgear for Electricians
#76192 02/06/01 12:34 PM
Originally posted by resqcapt19:
Electrican,
Were the circuits in your last post "3-wire" or "3-phase"? My understanding is that there is no neutral overloading or harmonic problems with nonlinear loads on 120/240 single phase systems.
Don(resqcapt19)
The circuits are 3 phase 120/208. Our temp. solution is to rewire the lab w/ dedicated neutrals. Only problem is this pushes the problem to the service conductors feeding the panel that feeds the equipment.
#76193 02/06/01 02:21 PM
doc Offline OP
well gents you all lost me at about post reply # 13 but it is sure interesting reading even though I haven't a clue about most of this ha ha
MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE
#76194 02/06/01 05:20 PM
Electician,
Don't forget that when you use individual grounded conductors for each circuit, all of the conductors are current carrying and derating in Table 310-15(b)(2)(a) will apply.
Don(resqcapt19)
Don(resqcapt19)
#76195 02/08/01 08:31 AM
Broom Pusher and
Don,
I sent a direct E-Mail to you [a reply] on this subject. Let me know if you did not receive it and I'll resend.
Once we get this figured out, I'll post the results to this thread.
Scott "S.E.T."
Scott " 35 " Thompson
Page 3 of 3 1 2 3