ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 89 guests, and 7 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 3 of 3 1 2 3
#74852 02/11/07 06:10 PM
Joined: Feb 2007
Posts: 5
E
Junior Member

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#74853 02/11/07 11:58 PM
Joined: Oct 2000
Posts: 2,724
Likes: 1
Broom Pusher and
Member
Here are a few Photos of Transmission and Distribution Circuits / Poles, for US systems.
These are located in various areas of ECN:

[Linked Image]

This shows a Wood Pole, which is carrying (I think) is one 3 Phase 66KV Transmission circuit (on the left), one 3 Phase 34.5KV Distribution circuit (top right), and a possible 4160Y/2400 3 Phase 4 Wire Distribution circuit on the lower section (the Transformer is fed from this circuit).

Behind the Wood pole is a Transposition spot, for a two 3 Phase 138KV - 230KV Transmission circuits.

To the left of the Transpositions is a 138KV 3 Phase 2 ciruit Transmission structure.

[Linked Image]

Here is an oddity: This is an Open Wye Primary, Open Delta Vee 4 Wire Secondary Transformer configuration.
The Primary Distribution feeders appear to be a 13200Y/7620V 3 Phase 4 Wire Wye system.

The Secondary is one of the "Famous" 4 Wire Deltas - with the "High Leg".
Secondary Voltage is 240/120V, 3 Phase 4 Wire Delta. Measured Voltage from the secondary bushing on the far left side of the smaller Transformer, to the center tap of the larger Transformer, will equal something in the range of 195-208 Volts, while measuring Voltage between the center tap and either the left or right bushings of the Larger Transformer, will result in 120V, and all L-L measurements will show 240V.

[Linked Image]

Here is a 4 wire Wye secondary setup, with a delta primary arrangement.
Primary side voltage is in the 4KV range (looks like 4160).

[Linked Image]

Here are some wooden poles (tilting drammatically), with two 66KV 3 Phase Transmission circuits on the upper sections, and a few 12KV 3 Phase Distribution circuits on the lower sections.

[Linked Image]

Here is a shot of some Transformers fed from what appears to be a 7200 Volt 3 Phase circuit.

[Linked Image]

Another 12KV Distribution pole.