0 members (), 227 guests, and 28 robots.
#69970 10/05/06 12:50 PM
There are 2 issues with swapping a wye for a delta. One is that delta is 240 between legs and wye is 208. The second issue is the high leg.
#69971 10/05/06 02:58 PM
Power always goes out they dont want there meat to go bad. Is ther an other way to go?
You could go with a 480 3 phase generator feeding a 480/240 wye delta transformer. Power up the genny off of the gas main if available, propane and tank, or diesel and tank.
I don't know if you can get a delta high leg in a single unit. If you can't, feed the 120 V loads from a single phase 240/120 transformer.
Larry
edit because I still don't have UBB down.
[This message has been edited by LarryC (edited 10-05-2006).]
#69972 10/05/06 03:40 PM
jersey Offline OP
the generators are gas. I assume all the equipment will work fine off the 208 voltage. so if there is a transfer switch and there are no 240 1 pole loads what would it be the problem with backing up a 3phase delta panel with a 3phase wye generator
#69973 10/05/06 03:47 PM
I don't think that might be a valid assumption.