ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 161 guests, and 8 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#65575 05/06/06 04:35 PM
Joined: Jul 2004
Posts: 625
S
Member
It was mentioned in another thread that, in some areas, municipalities and some POCOs are requiring a 22kA rating on residential services.

I've read Sq D's and C-H's documents on series ratings, and their panels are specified and tested such that a 22kA or 25kA main breaker in series with a 10kA branch-circuit breaker has an overall 22kA series rating.

But, these series ratings don't extend to three in a row. If you have a subpanel fed from a 10kA feeder breaker, those 10kA breakers in the subpanel aren't covered in the listing for the series rating; they only have their native 10kA rating.

To get to 22kA, you need to do one of two things: Either use a 22kA breaker for the feeder, or use 22kA breakers in the subpanel.

What I'm wondering is, what are people actually doing on subpanels in the areas that are requiring 22kA residential equipment? Are you installing 22kA feeder breakers, or just assuming that the 22kA main covers the whole thing?

Or is my understanding of three-in-a-row series ratings incorrect?

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#65576 05/07/06 03:18 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
My understanding is that the 22K main to 10K branch would be the same as a 22K main to 10K feeder to 10K branch.

OR- 22K main to 22K feeder to 10K branch.

Most of the lists, in panels or other documentaion I have seen, seem to reflect that.

And would accomplish the same thing. Really depends on the list of allowable breakers.... (Which seem to be, any that THEY make. [Linked Image] )

What I have always wanted to know is. If Company A claims thier 22k breaker will accomadate 22k for the 10k breaker of Company A. Why would it not withstand 22K for Company B's 10K breaker?


Mark Heller
"Well - I oughta....." -Jackie Gleason
#65577 05/07/06 05:09 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
I'm not aware of any maximum distance requirements between series rated devices, or a requirement to be directly adjacent in the distribution path.
If there is a fault downstream of the second 10kAIC breaker, the current will come from the first 22kAIC rated breaker and act appropriately.
Be sure there is no significant motor load downstream, because then the fault current downstream may be different than that seen upstream.


Ron
#65578 05/07/06 06:14 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Series ratings must be tested. I have never seen a tested rating on any "classified" breaker.

It is possible to have series ratings of 3 breakers. You can not "skip" a sub-feed breaker it must have been tested.