#60370 01/02/06 12:35 AM
Joined: Feb 2004
Posts: 1,438
Member
I've done longer pulls of 350MCM than this by hand X about 10 hands and we got it done.... but it still sucked....

#60371 01/02/06 05:06 AM
Joined: Aug 2005
Posts: 44
Member
It's Doable (I think that's a word)
Just make sure you use plenty of soap, and you better have someone who knows how to FEED the wire.
1 person properly feeding the wires will make a world of difference. Most hand pulls we do gets 2 guys feeding, 1 guy to pull the wires off of the spools and one actually soaping and feeding.


It's Not The Fall That Kills You...
It's That Sudden Stop At The End
#60372 01/02/06 10:39 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Quote
might want to think about 36" 90's
It would make sense that a larger radius 90 would make it pull easier, but that is not reflected in any of the pulling tension calculations that I have seen. The only time the radius is used, is to calculate the sidewall pressure (crushing force on the insulation as the conductors are pulled around the 90).
Don


Don(resqcapt19)
#60373 01/02/06 03:53 PM
Joined: Jun 2004
Posts: 92
P
Member
It is intuitive that a sweep should be easier to pull than a conventional 90º. I compare it to a gradual freeway offramp versus a 90º surface street corner. How do your calculators deal with a plumbing elbow with a 1/4" radius?
Those formulas were probably derived from tests using standard fittings. Has any research been done comparing them to larger radius sweeps? I would like to see this.
One small point, which I don't think should be debatable, is that it is harder to bend a cable into a smaller radius than a larger radius. Every time a cable is pulled through an elbow, it is bent and then also unbent. This alone should add a certain amount of extra force required.
The next time I get a job involving a lot of conduit, I will invest in an Ericksen bender.
~Peter

#60374 01/02/06 07:23 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Pete,
They are not my calculations. They are the standard calculations for wire pulling tension that were deveoloped by the Insulated Cable Engineers Association.
Here is some info.
Don


Don(resqcapt19)
#60375 01/03/06 01:57 AM
Joined: Jul 2002
Posts: 717
M
Member
You know with that size wire, you might be able to push the thing thru instead of pulling it.

#60376 01/03/06 08:53 AM
Joined: Sep 2003
Posts: 650
W
Member
Ya know where the same formulas are used? Bicycle brake cables. Bends are bad. Lube is good [Linked Image]

Remember that science as all about creating approximate descriptions of the physical universe, testing these descriptions, and refining them. Very often, one finds an approximation that 'works well enough', and just uses that approximation to 'do stuff'. This is where science becomes engineering [Linked Image]

To a very good approximation, friction does not depend upon contact area. Instead friction depends upon the materials involved, and lubricant between them, and the total force pushing the materials together. If you double the contact area, you double the area available to create friction, but halve the force per unit area, net result total friction remains constant. Again, this is an approximation; in the real world increasing the contact area might increase the friction because there are more places that can stick together, or reduce friction because distortion of the objects gets reduced. But for calculating cable pulling force, it is generally 'good enough' to consider only materials and contact force.

For straight horizontal pulls, the contact force is caused by the weight of the cable.

But when you go around bends, additional force is caused by the tension in the cable pulling it against the bend. Consider a 90 degree turn; you have the drag of the cable in the conduit pulling 'west' (for example), and the tugging force pulling 'north', and the cable is getting squashed against the side of the bend with force to the north-west.

The total contact _force_ caused by the bend in this turn depends only upon the total cable tension and the angle of the turn, but not the radius of the curve. This gets us back to the approximation that friction depends only upon the materials and the pressure, but not the area.

If you increase the radius of the curve, then you get less contact _pressure_, and thus less friction per unit area, but more total area, and thus approximately the same total friction.

This approximation clearly falls down on a number of points. For example, it ignores the stiffness of the cable. Clearly, a larger bending radius means less effort in _bending_ the cable, even if it means the same contact pressure and thus the same sliding friction. It also ignores things like distorting the insulation, or high pressure displacing the pulling lubricant. But it also ignores any 'stickiness' in the lubricant, which might actually _increase_ the friction if the radius of the bend increases.

Since a bend causes friction, which means tension in the cable, and the friction in a bend depends upon the total tension, multiple bends creates something of a multiplying effect; each bend will produce friction that depends upon the friction leading up to the bend. This is why cable pulling tension can be different when going in different directions, and why multiple bends is bad; double the bend and get 4x the bend friction. Also because of this multiplying effect, even slight reductions in friction (using lube) will result in major reductions in total pulling force.

-Jon

#60377 01/05/06 12:30 PM
Joined: Apr 2005
Posts: 116
X
Member
I agree. There are many tricks of the trade that calculations can't help you with, either. 36" 90*s, pulls are better through rigid 90*s than pvc, swabbing the conduit with a soapy rag before the pull, etc. On long underground runs, I like to blow the conduit out with an air compressor. I've blown out welding rods, soda cans, and trash before, not to mention the water that accumulates in it.

#60378 01/13/06 05:43 AM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Definitely want to use a rope with "minimal burn-in qualities", when pulling through PVC ducts.

What I am referring to is how ropes will dig into 90° elbows, and burn themselves in - eventually adding resistance to the pull in an exponential fashion.

Just my 2¢

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!