ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 117 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Jan 2005
Posts: 5,485
Likes: 5
Cat Servant
Member
Wolfgang, we do things a little diffeent here.

Our "220" volt circuits are created by using two 110 legs that are 'out of time' with each other; this contrasts to your use of a 220 leg with a neutral wire.

In our 208 three phase set-ups, we have three legs that are each only 120 to ground, plus a neutral. The 120 circuits are simply drawing from just one leg.

Where the actual three phase power measures out at 240, the individual legs will likely measure out as 120, 120, and 208 volts respectively. In that case, you must be vcareful as to which leg you take your 120 from!

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Sep 2005
Posts: 153
W
Member
@ renosteinke:
Thanks for the answer. I have already seen those schemes with transformers tapped in the midst of one leg. So I have no problem with the details given for the small installation in this thread, assuming the 2 hot wires are at 180° of a single phase transformer (or single leg):

Quote

" 1 phase, 60 Hz., 230 volt, 2 hot wires plus a neutral and a ground wire

but I wondered how does one provide 460V, 230 V and 115 V at the same time out of one transformer in three phases:
Quote
3 phase, 230/460 volt, 60 Hz., 3 hot wires plus a neutral and a ground.
The timer, alarm and control system on all units are always 115 volts single phase powered.

As all voltages are linked here by factor 2 and not 1.73, what is three phase here? Or is a second transformer involved?
Thnaks for your patience.

Joined: Dec 2000
Posts: 4,294
Member
The "230, 460" portion will be 230 or 460 volt. The motors come with 9 leads, and the windings can be connected either in series or in parallel.

The "115" portion could be taken from the same transformer for the 230 volt system, however the "460" volt version would require the control voltage to be taken from another source.
I don't understand why they would want a "neutral" to be run with the 460 volt system, as this would provide 277 volt power.

The actual 3Ø system voltages are nominally rated as:
120/208 Wye
120/240 Delta
277/480 Wye
and although they are becoming less common, there are still some 240 and 480 delta systems out there that provide no "neutral" at all.

Joined: Sep 2005
Posts: 153
W
Member
Now I got it, thanks a lot. Doesn't sound very "harmonized" yet.

Joined: May 2005
Posts: 706
T
Tiger Offline OP
Member
The designer made an error on the plan. L1 and L2 are 230-volt single-phase, and L3 is 115-volt single phase. There is no 3-phase circuit. In two emails the guy still hasn't told me the amperage requirements for the two circuits.

This is like receiving a machine arrive in 15 parts with no installation instructions other than a print with who-knows-how-many errors in it.

I think this guy enjoys travel with all expenses paid by the customer.

Dave

Joined: May 2005
Posts: 706
T
Tiger Offline OP
Member
I got some cut sheets for the pumps today, so maybe I'm being impatient. I'm still trying to find out if it's OK for the 230-volt pumps to run at 250-volts, or if I need to drop the voltage with a transformer.

Dave

Joined: Jan 2005
Posts: 5,485
Likes: 5
Cat Servant
Member
Tiger, NEMA standards typically allow for + or - 10% of the rated voltage for motors. So running "230" motors on 250 volts actual should be fine.