I need to install a disconnect in very limited space for for a 4.5 KW water heater. Any recommendations for a small footprint disconnect.
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
4500 / 240 = 18.75 amps.
How about a 30 amp rated two pole switch, it will fit in a single gang box.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
|
Joined: Feb 2004
Posts: 133
OP
Member
|
That would work except the switch is going to be mounted under a vanity and I'm afraid a standard toggle switch might be inadvertantly turned off as items are placed under there for storage. For that reason I was leaning towards a pull out disconnect.
|
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
You could install a WP single receptacle cover on the switch to protect it.
Curt
[This message has been edited by caselec (edited 05-31-2005).]
Curt Swartz
|
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Is this for that steam unit?
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
|
Joined: Feb 2004
Posts: 133
OP
Member
|
|
|
|
|
|
|
Joined: Apr 2005
Posts: 27
Member
|
The smallest 30 A disconnect I have seen is roughly 6"wide by 6" high and around 3" thick. Your best bet is the toggle switch with an off the shelf W/P cover like caselec suggested, I don't think you can get any smaller than that. If you want to get fancy try one of these http://www.newark.com/product-details/text/CD121/4907.html
|
|
|
|
|
Joined: Feb 2004
Posts: 133
OP
Member
|
Or one of these should do the trick: http://www.improvementscatalog.com/Parent.asp?product=158489x&dept%5Fid=0&subdept%5Fid=40
Thanks for your input.
|
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Still trying to figure out what part of the code these "steam units" fall under. See the code forum.
424 requires: Disconnect within site of equipment or controler, and in some cases be able to locked open.
And 427 requires: "disconnecting means shall be of the indicating type and shall be provided with a positive lockout in the “off” position."
Sounds like either way it may need to able to locked open.... Then again I have always done them with a lockable fusable disconnect switch, when I thought they were under a different code....