0 members (), 510 guests, and 152 robots.
#52458 06/03/05 04:17 AM
e57 Offline
Oh, you can use 1" only for signage only service's.
#52459 06/03/05 10:49 AM
The service is thru a meter center. Their local requirements is normally 1 1/4 but the inspector said they would allow 1" for this building.
#52460 06/03/05 10:52 AM
Getting #3 at the supply house is no problem here. Last I checked #3 was not much cheaper then #2. But it adds up if you need a lot.
#52461 06/03/05 12:06 PM
when you say "meter center" is this a meter bank with disconnects built in ? If so won't you need a ground also?
#52462 06/03/05 01:50 PM
Yep a meterbank with discos. Equipment ground not required for RMC & EMT. Would like to run one. Can do 3 #3's +#8 in 1" but not #2's. Whish I was doing it and not writting about it right now.
[This message has been edited by Active 1 (edited 06-03-2005).]
