ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 536 guests, and 33 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#51559 05/02/05 06:19 AM
Joined: Aug 2001
Posts: 335
S
Member
GFCIs don't work on multiwire circuits because of the shared neutral ... how about AFCIs? Anybody tried? I've learned things the hard way too many times. Figured I'd ask before screwing up.

Joined: Nov 2000
Posts: 2,148
R
Member
Same as GFCIs...you can get expensive 2 pole ones that work on mulitwire circuits.
Don


Don(resqcapt19)
Joined: Feb 2005
Posts: 693
L
Member
Just to cklarify, you can use a multi-wire circuit with GFCI protection as long as you split the neutral where the GFCI's are fed.

That is, by using receptacles, not breakers (unless they're breakers in a sub-panel, in which case, the 'multi-wire circuit' is actually a feeder.)

In other words, the 'load' terminals must have separated neutrals; they can share a single neutral at the 'line' terminals.

I've done this where a jetted bathtub required two GFCI receptacles, for motor(s) and heater. I ran a 12-3 rather than two 12-2's.