#5122 11/04/01 08:02 AM
Joined: Dec 2000
Posts: 4,294
Member
In drilling standard wood beams, the rule of thumb out here has been to keep the holes within the outer 1/3 of the spans. Most inspectors like them within a foot of the supports. Drill through the center of the span, and you'll be buying somebody a new beam.
Gluelams, as used in our tilt-ups, are seldom drilled, as you can normally pass under them.(They aren't as strong as they look, they only hold up the roof)
For Engineered wood products, such as TJI joists (the waferwood or plywood jobs with a top & bottom chord) we always have to contact the manufacturer for their requirements, as they can vary.

#5123 11/04/01 09:24 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
Bill,
The beam runs from the rear of a townhouse forward. I don't know how long it is, but I drilled a 5/8" hole about 2-3" from the bottom, and about 24" from the end. I doubt that any appreciable harm was done, although during construction I'm sure that everyone can't just indiscriminately drill as they please. However, I wanted to get some opinions for future reference.
Thanks, everyone.

[This message has been edited by Redsy (edited 11-04-2001).]

#5124 11/04/01 11:02 AM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Electure,

Are we talking about the same stuff?
Quote
Glulam has greater strength and stiffness than comparable dimensional lumber. Pound for pound, it’s stronger than steel. That means glulam beams can span long distances with minimal need for intermediate supports. It also means that designers and builders have virtually unlimited design flexibility when using glulam, whether the application is home construction, a commercial warehouse roof or a highway bridge.
http://www.apawood.org/glu_level_b.cfm?content=prd_glu_main


Bill
#5125 11/04/01 11:54 AM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Redsy,

Yes, it looks like you really can't just drill any size hole wherever you want it.

I found some good info: (get PDF at end)
http://www.anthonyforest.com/stockfaqs.htm
(cautions to read the following before notching, drilling, etc.)
Quote
General Guidelines:

A. Holes: Cannot exceed 1 1/2" in diameter. Limited to certain zones. Refer to Drilling and Notching Technical Note.

B. Notching: Absolutely no notching on tension side (usually bottom of beam).
Top of Beam - Notch on top with limitations (see Technical Note).
Beveled cut or slope cut for roof line - Generally the depth of notch on end of beam over outside bearing cannot exceed 40% of the beam depth.
**************************************
[Linked Image]

This comes from a 6 page PDF file that looks pretty good entitled: "Field Notching and Drilling of Glued Laminated Timber Beams"

Note:
The construction of these things are not uniform, so there are zones that are definitely better than others.

Get PDF File

Bill

[This message has been edited by Bill Addiss (edited 11-04-2001).]


Bill
#5126 11/04/01 11:58 AM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
When requested to replace said beam, I would simply request to see my contract...

There are advantages to the "no contract" way of doing things...

I've drilled 2" holes in glue-lam... If they didn't like it they can find somebody else...


Muahahahahahaha! (Evil laugh)


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#5127 11/04/01 12:14 PM
Joined: Oct 2001
Posts: 597
E
Member
Wow!

That's really different than plain old Wood!


Al Hildenbrand
#5128 11/04/01 12:17 PM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Al,

That's a interesting PDF file. isn't it?

Bill


Bill
#5129 11/04/01 01:04 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
Bill,

THANKS!
That was EXACTLY what I needed.

#5130 11/04/01 04:46 PM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Redsy,

It looks like you drilled in a good spot!

I've only done custom resi work and many times these beams are waaayyy oversized and drilling wouldn't be as critical, but it is good to know this information anyway. They probably oversize just to be sure and don't care as much about cost because they are not buying a lot of them. I'd imagine that in situations where many beans are needed (many similar structures going up, Condos, Townhouses, etc.) for economic reasons, they would be sized more closely to the load served and therefore have less tolerance to field modifications.

Bill

[This message has been edited by Bill Addiss (edited 11-04-2001).]


Bill
#5131 11/04/01 07:53 PM
Joined: Dec 2000
Posts: 127
G
Member
This is from the 1988 UBC. I do not have a later version but should be similiar.

Notching and boring for wood joists that are structural members:

Notching can't be done on middle third of the joist.
Notches on the end can't exceed 1/4 the joist depth.
Notches in the top or bottom between the end and 1/3 joist length can't exceed 1/6 the joist depth.

Bored holes can't be within 2" of the top or bottom.
Bored hole diameter can't exceed 1/3 joist depth.


Gerald Powell