1 members (gfretwell), 377 guests, and 12 robots.
#49666 03/12/05 05:22 PM
Does anyone know how to test for harmonic distortion without purchasing and expensive testing instrument. I priced one for around $4000 ouch... need an alternate method. one of the schools that we work in is blowing power supplies in their computers and their engineer thinks it might be caused by harmonics. I would like to test over time, like a chart recorder would be used.
Take at look at the TPI 440 Scopemeter. Around $300.00 on sale.
Al
Here is the meter Al is talking about.
[Linked Image from kilowattclassroom.com]
You can check it out here.
http://www.kilowattclassroom.com/Equip440.htm
That said I have never heard of harmonics damaging a power supply does anyone have any info on that?
Bob
I believe that if you are only looking for "qualitative" testing (i.e. whether or not harmonics exist) and not "quantitative" testing (an actual value of distortion), and you already own an average sensing and a True RMS amp meter, you can determine if harmonics are present. http://support.fluke.com/find-sales/download/asset/1260362_k_w.pdf
Other than that I have rented sophisticated logging analyzers several times and they are not that expensive overall.
http://www.us-instrument.com/
Look at the "Dranetz" products
[This message has been edited by Redsy (edited 03-12-2005).]
e57 Offline
PC supplies are pretty tolerant of power line problems. The first thing they do is convert to 160v DC and chop that to 25kz square waves. They make harmonics. It doesn't see harmonics.
BTW the quick and dirty is to use a clamp on the neutral. Harmonics (power factor etc) are the difference between the actual current and the expected current if you had a clean load.
Measure current with standard amp-clamp. Measure again with "true RMS" amp=clamp. More than 15% difference is enough to start worrying about.
And- remember- there are no harmonics on single phase systems.
Why don't you think there are harmonics in single phase systems? The triplen harmonic isn't as big a problem but you can certainly have harmonics.
Greg the damaging harmonics cancel each other out on a single phase supply system as in a 120/240 system.
Only from a 3 phase supply like 208Y/120 do you need to worry about overloading the neutral with harmonic currents.
Bob
He wasn't talking about overloading the neutral, they said the harmonics were damaging the PC supplies. You can have nasty harmonics on a single phase system but I still don't think it will hurt a switcher supply. I won't get into whether a situation where current lags voltage by 8ms could exist.
