0 members (), 723 guests, and 19 robots.
#49080 03/03/05 08:00 PM
Whatever you do don't put general room lighting on an afci with your outlets. All it takes is one ceiling fan to become a real pain in the you know where. Don't ask how I know that ok?
It does not matter if you win or lose but how you lay the blame :-)
#49081 03/03/05 08:55 PM
I had a service call yesterday on a house I wired in March 2002. The bedroom wiring is protected by 1st generation AFCI breakers that I installed.
The owner knocked a lamp over in the bedroom and the bulb broke as it slamed to the floor causing the AFCI breaker to trip. Of coarse the yuppi homeowner was not able to find the tripped breaker.
Nice easy service call [Linked Image]
I can't be sure what part of the breakers protective circuitry caused it to trip...
Was it an arc or a shortcircuit from the bulb smashing that caused the breaker to open?
I can tell you that I do have ceiling fans, florescent closet lights and smoke detectors on these AFCI circuits without any problem call backs ever.
shortcircuit
#49082 03/04/05 10:29 PM
You must be lucky then,
I changed the way that I wire houses based on our problems in a large apartment building that was done. I don't know if it was the type of AFCI or maybe the fans but everytime the fans were put on they would trip about half of the AFCI's what a pain.
#49083 03/07/05 12:39 AM
is it ok to install gfci recp. at 1st rect hole instead of arc fault breaker in the load center??
#49084 03/07/05 05:47 AM
I thought everything in dwelling bed rooms had to be afci, plugs & lights?
not smokes?
#49085 03/07/05 09:00 AM
Everything in the bedroom has to be AFCI, "all outlets" including smokes. I have even seen debates saying the outside light has to be AFCI if the switch is in the bedroom ... YMMV on that one.
#49086 03/07/05 01:51 PM
What type of AFCI breaker is it? Square D has a recall on theirs. We have also had problems with motor loads on these circuits, especially with exercise equipment.
#49087 03/07/05 02:06 PM
Here are the recall notices for the Square D products:
Consumer product Safety Commision (CSPC) ~ http://www.cpsc.gov/cpscpub/prerel/prhtml05/05035.html
Square D ~ http://www.squared.com/us/squared/corporate_info.nsf/unid/9CB09A222974952E85256F19005EAE4F/$file/afcirecallFrameset.htm
~~ CELTIC ~~
...-= NJ =-...
#49088 03/07/05 04:59 PM
I've been doing this since 2002; 25+ homes a year, and nver had a problem. I must be lucky, too. [Linked Image]
#49089 03/07/05 07:28 PM
I have heard a big part of the "fan problem" is leaving too much exposed insulation exposed on the usual neutral wire cludge and it shorts to ground when you shove all that stuff back in the box. In a regular circuit that will go unnoticed but the GFI function of the AFCI will trip.
