#48314 02/09/05 11:18 AM
Joined: Feb 2005
Posts: 1
S
swampy Offline OP
Junior Member
I 'm studying for my Journeyman's. One question is ; A 10 kva trans. is 240/120v. step down. secondary ocp is 125%. What is max. cb required for primary if eff. is 100%?

Can anyone give me some pointers? Thank you!

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: May 2004
Posts: 162
C
Member
The formula for pri current is kVA/E pri times the phase multiplier. In this case a single-phase multiplier is 1. If it were 3 phase the multiplier would be 1.73.

It would be a good idea to read section 450.3(B) and study the table. You should understand that in general a transformer operating at 600V or less is considered (in general) when the pri OCPD is set at 125% of the pri FLC) The table will go on to indicate that in cases where there is OCP at the secondary of the transformer which is set at 125% of the secondary FLC, the pri OCPD may be increased to 250% of pri FLC.

Your transformer should have a 41A pri and 2.5 X 41 yield 102. (see notes to tables ) I'd call it 100A.

Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
Cpal said "Your transformer should have a 41A pri and 2.5 X 41 yield 102. (see notes to tables ) I'd call it 100A."
That is correct. Note that the table allows you to go up to 250% but not exceed that figure. If the 250% does not yeild a standard
fuse or breaker, you may not round up.