To save some transformer capacity, it may be possible to obtain a 208—120/240V 1ø drytype, connected in a split autotransformer configuration.
www.acmepowerdist.com/pdf/Page%2055-63.pdf PRIMARY: 208 SECONDARY: 120/240 TAPS: 2, 5% BNFC
480V discharge fixtures should operate acceptably down to about 440V, although cold weather or motor starts on the 208V system my complicate this. If nonimal 208V runs low, moving the transformer connection from H4 to H3 will increase output voltage. {Its normal for 150°C-rise drytypes to run
very hot—they should always be mounted in an area with adequate ventilation and clearances as labeled.}