ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 419 guests, and 6 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#47072 01/08/05 12:22 AM
Joined: Dec 2004
Posts: 46
T
ToHo Offline OP
Member
Customer has 200amp OH service w/ 2 100amp meters(double gang meter) feeding 2 100amp panels w/100amp main breakers.Customer wants one panel to be up graded to a 200amp.So the end result would be a 200amp & 100amp panel. I would think I would have to upgrade to a 2 gang 200amp meter box.The house has gas heat and appliances. The load calculation on the house isnt changing by a large amount. Just needs more breaker space for attic renovation.That said ... the 200amp OH service should be ok.. any input is greatly appreciated..ToHo

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#47073 01/08/05 12:40 AM
Joined: Sep 2004
Posts: 86
N
Member
You would have to upgrade to the two 200 amp meter sockets. Sounds like a lot of work if the loads aren't changing. How about installing a 30 circuit 100 amp main breaker panel and upgrading the grounding? SQD makes one and I believe Cutler Hammer does to.
Ron

#47074 01/08/05 12:48 AM
Joined: Dec 2004
Posts: 46
T
ToHo Offline OP
Member
customer wants the 200amp panel for future use if necessary. I don't believe The utility Co. rates the residential service as a continuous load?(only commercial) I'm not sure at what point the utility Co. would want me to upgrade the 200amp OH service. ToHo

#47075 01/08/05 03:05 PM
Joined: Nov 2002
Posts: 267
W
Member
You may want to consider the Milbank number
U2601-XL. It's a 2-gang horozontal one 100 amp and one 200 amp. Now you can have a 200 amp main 40 ckt on one side and a 100 amp 30 ckt on the other. They're mostly used where there's one larger sq ft home next to a smaller apt/in law.

#47076 01/08/05 10:38 PM
Joined: Dec 2004
Posts: 46
T
ToHo Offline OP
Member
wirenutt..
thanks..I did not know milbank made a combo meter enclosure like that.. I just have to check with the poco to see if 4/0 seu service riser will be large enough for both services.. Thanks again ToHo

#47077 01/09/05 01:14 AM
Joined: Sep 2004
Posts: 86
N
Member
Hey Wirenutt,
35 years in the business and thats the first time I've heard Milbank had such a meter socket. Very interesting. Will have to see if WE energies approval is on that one for future use. Education never comes to an end.
Ron

#47078 01/10/05 09:40 PM
Joined: Nov 2002
Posts: 267
W
Member
I didn't know it was made til I had started working in a supply house. After years in the field now have acsess to all this info., figures, LOL....

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5