#46994 01/08/05 01:19 AM
ya I looked at that. it's really great.
1/2 emt and 1" gal come both in ten foot sticks.
#46995 01/08/05 03:15 AM
?yllamron daer cixelsyd deye-ssorc a seoD
LOL,
nayR! [Linked Image]
[This message has been edited by Trumpy (edited 01-08-2005).]
#46996 01/08/05 10:51 AM
Here's one:
You have 118 feet of two inch rigid between the panel and the box. What is the minimum number of straps required to support it?
I think the pipe question got ya tho.
EMT is ten feet without the coupling rigid is ten feet with the coupling, making them 9'11".
#46997 01/08/05 11:37 AM
Anonymous
Unregistered
Hey bucket, I have found most of the folks on this forum to be pretty durn good people and very helpful. So I hope some of the posts on your thread don't take you back.
( I think they get more friendly as you get further and further from the East Coast. [Linked Image] )
Your answer to my question is not correct.
Should be 200.7 (C)(2)
I have been looking around for that for a couple days though. Thanks for doing my home work! [Linked Image]
#46998 01/08/05 11:52 AM
What is the maximum number of conductors one may place inside EMT Conduit?
Please give number of conductors, size of conductors, size of EMT, and OCPD size assuming non-continuous loads.
Hint: This Calculator may help...
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#46999 01/08/05 02:38 PM
( I think they get more friendly as you get further and further from the East Coast. )
OUCH!!
#47000 01/08/05 02:47 PM
Bill I concur!!! double ouch!!!
Sun Tzu wrote in the 'Art of War', about 2300 years ago - do not under estimate your enemy. I say do not under estimate your friends, including us Easterners [Linked Image] [Linked Image] !!!
Pierre
Pierre Belarge
#47001 01/08/05 04:12 PM
"What is the maximum number of conductors one may place inside EMT Conduit?"
singl or three phase?
1" emt @ (24")
#12 awg
20 amp ocp
# of thhn conductore are 26
1"emt @ (25")
#12 awg
20 amp ocp
# of thhn @ 75c conductore are 6+ground unbalanced
-single phase 9+gound balanced
-three phase 8+gound balanced
#47002 01/08/05 06:42 PM
What 3 IBEW locals make the most money per hour?
#47003 01/08/05 08:27 PM
e57 Offline
Does this comply? State NEC refferance.
2 Bx off-sets, 3 - 90's, 2 - 45's on the same run of conduit.