0 members (), 761 guests, and 9 robots.
Page 3 of 7 1 2 3 4 5 6 7
#47004 01/08/05 08:29 PM
Local3Jr,
What 3 IBEW locals make the most money per hour?
are you going to give us an A,B,C,D, choice? [Linked Image]
Welcome to the forum, but Union or Nonunion affiliation is a blind issue here.
Roger
#47005 01/09/05 01:36 AM
Local3Jr,
I agree with Roger, leave that out of this....
{Sentence removed by Webmaster}
Dnkldorf: Let's not stir anything here.
[This message has been edited by Webmaster (edited 01-09-2005).]
#47006 01/09/05 01:54 AM
Dnk,
Someone is not a word. I think you meant to say some one.
#47007 01/09/05 02:39 AM
Local3Jr,
In case you don't know, We're a mixed group here, we don't talk about affiliations. We focus on the Codes and doing the job better and safer.
With that said, Welcome to ECN.
#47008 01/09/05 04:38 AM
State NEC ?
the national electrical code 344.26
not more then 360 between pull points.
#47009 01/09/05 06:06 AM
e57 Offline
Yep, Box off-sets count too!
You have no idea how many times I say that to people that have been at this for years.
And I'll take a stap at Local3jr's Q?
Chicago, SF, and NYC. If not LA.
#47010 01/09/05 11:17 AM
Yes, let's say three-phase...
(Oops-forgot that little important issue)
Hmmm...
I get 161 #8's in a 4" EMT non-cont rated will net me 17.5A and a 20A Breaker.
Correct?
-Virgil
5 Star Inspections
Member IAEI
#47011 01/09/05 02:48 PM
711- 14 AWG type Z conductors in a 4 in EMT conduit, as per Table C1 - page 646 NEC 2002.
Using a 6 amp fuse as per 240.6(A) - This is feeding many motors [Linked Image] [Linked Image].
Pierre
[This message has been edited by PCBelarge (edited 01-09-2005).]
Pierre Belarge
#47012 01/10/05 01:31 AM
In a 2 story dwelling do you need smokes down stairs even if there is no hallway?
In a basement you have 2 exits does code require lights to be on 3, ways
If you have an ISO ground bus in a sub panel can you take this wire and bond it directly to the cold water pipe?
When wiring an Elevator when and why do you a Shunt Trip Breaker?
3 phase 480v A/C unit has a 600V disconnect slow blow fuses does the breaker still need to be HVAC rated?
How many breakers are allowed in an out building sub panel before you need a main disconnect on that sub panel.
The foreman tells you; above the ceiling is a conditioned space. Does this mean you have to use compression fittings? What about phone and data cable, fire, class 2 wires? Does it need to be in EMT?
#47013 01/10/05 07:23 AM
Dnkldorf: makes no difference