#43548 10/16/04 10:52 PM
Joined: Nov 2002
Posts: 244
W
Member
I agree with Electric eagle. The code section he refered to, allows you to use conduit to protect the wire. It doesn't say you have to break the conduit every 4 1/2 feet to staple the wire or break the conduit to staple the wire at the panel. I use the fitting that is both romex connector and EMT connector on the attic side and terminate the EMT at the panel as usual. I have never been called on it and have not lost a bit of sleep worrying about it either.

#43549 10/16/04 10:55 PM
Joined: Oct 2001
Posts: 597
E
Member
I think the key is 334.10(A)(1). Exterior conduit is a wet location.

Well, you are in "arid" Arizona. . .


Al Hildenbrand
#43550 10/17/04 08:35 AM
Joined: Apr 2004
Posts: 201
Member
Are you saying it never rains in Arizona so the outside of the home is not a wet location? [Linked Image]


Charlie Eldridge, Indianapolis Utility Power Guy
#43551 10/17/04 10:49 AM
Joined: Apr 2001
Posts: 507
G
Member
I believe the 2005 NEC will allow romex in conduit in the situation that aldav53 describes.

#43552 10/17/04 11:09 AM
Joined: Dec 2003
Posts: 751
E
Member
All conduit run out of doors is by definition (see Chapter 100) a wet location. Any conductors run in said conduit must be of the "W" type. NM is not, UF is. You could run UF indoors as well as outdoors, or do as you first thought, and switch wiring methods to THWN (not THHN) for the outdoor portion.

If the bottom end is open, it would drain any condensate that may form. (there are fittings designed for this purpose, or a small weep hole could be drilled in the bottom of the LB, in either case the entry into the panel would have to be sealed with duct-seal). It would be a simple matter to keep the conduit run from collecting any rainwater by the use of a gasket on the LB, and the use of raintight fittings, or by the use of PVC.


Earl
#43553 10/17/04 12:54 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
I use comp fittings with emt, so the NM is raintite. It enters a raintite outdoor panel. I put duct seal around the connector where it enters the panel and where it enters the soffit as an extra measure.


The Golden Rule - "The man with the gold makes the rule"
#43554 10/17/04 02:59 PM
Joined: Oct 2001
Posts: 597
E
Member
Aldav53,
Quote
From 2002 & 2005 NEC Article 100

Location, Wet Installations under ground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
If the EMT is on the outside wall, NM isn't allowed in the location. The only modifier will be if the location is "protected". One might argue that an eave overhang of some distance is sufficient to protect the raceway of such and such length from the weather.

G.J., 334.10(A)(1) is unchanged in 2005. NM must still be installed in "normally dry locations."


Al Hildenbrand
#43555 10/18/04 09:18 PM
Joined: Jun 2003
Posts: 1,143
D
Member
In the attic - NM on one side of a 1900 (4" junction box), other side FMC (Greenfield), transition to EMT above the soffit on the exterior wall...

Hey, if I could fit a few more adapters in ther I would... [Linked Image]

#43556 10/19/04 05:11 PM
Joined: Jun 2004
Posts: 220
T
Member
I think you could do it under 312-5(C) EX. The only thing is the pipe can't penetrate a structural ceiling, but this is a soffet. Would this be the same thing?

#43557 10/19/04 09:06 PM
Joined: Dec 2003
Posts: 524
Member
... This has been a note of contention I'd addressed on this forum once before.I had asked about it because there comes that time,when running a circuit in an unfinished basement,where you come down the wall with Romex,and you want it to be safe and look half-way decent,you sleeve it in pipe.You use a "from-to"... [Linked Image from bptfittings.com] and I was told that that was wrong to do,...mainly because Romex is not rated for wet/damp locations...I must admit,..I still continue to do this,as I believe that if it's in conduit,..it's not exposed to the dampness/moisture,..etc. the same thing goes for running short lengths of Romex thru Liquid-Tite,outside,..as for an A/C unit..the wire is totally protected,grounded,bonded,and goes from the disconnect thru the Liquid-Tite,to the unit,and is protected from the elements therein,...why the problem??? Please clarify
Russ


.."if it ain't fixed,don't break it...call a Licensed Electrician"