Just because one engineer did not know what the available fault current was does not mean that another doesn't know. In many cases, you could get an inexperienced engineer (or a lazy one) that doesn't know and doesn't want to ask someone else.
We will give the worst case like 77,000 amperes at the secondary bushings, assuming an infinite bus and a bolted fault. We will
not give the available primary fault current because we have a dynamic system. The bank may be fed from one substation today and another one tomorrow.
We will size our transformer bank at around 50% of the actual service size. For instance a 1200 ampere service at 480 volts will have a transformer sized for about 500 kVA of demand.
The reason for the 200 kA in NYC is that several different transformers will feed into the fault at the same time since they use a networked system.
Utility guy from Indianapolis