was is the allowable ampacities for 18 awg thhn
|
|
|
|
|
Joined: May 2001
Posts: 717
Member
|
Not allowed for General use, they are allowed for Fire Alarm systems (and a few other exceptions), the ampacity given in 760-23 is 7 amperes, and 6 amperes (from table 402-5) from 760-27
|
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Table 402.5 list 18 AWG at 6 amps, but as George said, 18 AWG is very limitted in its use.
THHN is not listed as a fizxture wire, but TFN and TFFN seem to have similiar characteristics.
What is this being used for?
Ryan Jackson, Salt Lake City
|
|
|
|
|
Joined: Feb 2002
Posts: 56
OP
Member
|
this was the question my foreman gave me. So i looked it up but was using table 310.15 and was confused, so i decided to ask you guys
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
It is listed as 14 amps @ 90 C in 310.16.
Now what can I conect it to that is rated 90 C?
310.16 shows no rating for 18 AWG @ 75 or 60 C.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|