zapped208,

Stop. Receptacle boxes in the floor gotta be approved for use as floor boxes. Check article 314.27(C). You cannot use regular wall boxes.


Earl
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: May 2004
Posts: 6
S
sbw010 Offline OP
Junior Member
I think I'll do something like e57's picture shows (thanks e57). I'll just strap a pvc 90 to the concrete form where it will end up in the "Sleeper Recess" from there I will take the earlier suggestions, and pipe over to where i'm going to mount the boxes, and fasten some type of floor box directly to the sleeper.

I'll have to do some research on what kind of floor box will be best for this situation.

Thanks to everyone for their suggestions
Stan

Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Not just the box to be rate, but plate too.

It must be able to withstand a 400 lb person standing on one high heel shoe!

Or something to that effect. No there are specific box and plate ratings out there.... Some for in use too!


Mark Heller
"Well - I oughta....." -Jackie Gleason
Joined: Feb 2003
Posts: 198
Z
Member
Just saw it at the supply house this morning.... a floor recep from P&S (pass & seymour) Brass plate, single recep & STANDARD 3 1/2 " sw box included. FWIW.


Shoot first, apologize later.....maybe
Joined: Apr 2003
Posts: 362
Member
P&S makes a floor receptacle that will fit on a standard box. Use one of the adjustable single gang side mount boxes. or a new smart box would work after the fact.

Phil


Choose your customers, don't let them choose you.