I've run into clients, in the past, who have paid attention to the wrong (or incomplete) information. They hear someone say: - 3 Ø motors are more efficient
- 3 Ø motors are quieter
- 3 Ø motors are simpler, less moving parts, therefore are more reliable
- yada yada
The client fixates on the "little truthes" without realizing that there is more that the 3 Ø motor involved. The client has to be educated about added complexity of the 3 Ø converter itself, the added equipment and installation cost. In my experience, the client doesn't want the education. . .in fact will push for the bottom line in an eternal quest to save money. The client's confusion results in the HVAC guys having to quote several prices for different systems, and the EC also having to quote several prices. Then, with all these different quotes, the client trys to find the cheapest combination. Russ, if the resturant cooling load is 60,000 BTU (can I assume that?) then tell the guy to stop the order for the 3 Ø equipment and rethink the project. In my opinion, equipment for converting 1 Ø to 3Ø is of value only when one is stuck having to use 3 Ø equipment (because nothing else is available) on 1 Ø power (because nothing else is available).
Al Hildenbrand
|
|
|
|
Joined: Jan 2004
Posts: 105
Member
|
As was said before, this application of phase converter is uncommon because the HVAC is normally a design item-it wouldn't be designed to be 3 Ø in a 1 Ø area. The only ones I have sold are used for a specific piece of equipment that was obtained(mill, stamper, autoclave, etc.) and the shop was only 1 Ø. You can get a price pretty fast, and I think that, along with conversion power loss, may change his mind. Good luck.
|
|
|
|
Joined: May 2001
Posts: 717
Member
|
Remember one of the first rules of Electricity: You can NEVER do better than your original source. Otherwise, all of us in this trade would have a 480 volt transformer in our houses.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
ElectricAL I think you hit the nail on the head. The client's confusion results in the HVAC guys having to quote several prices for different systems, and the EC also having to quote several prices. Then, with all these different quotes, the client trys to find the cheapest combination. You may have a semi electrical savvy HVAC tech telling the customer that 3 phase draws less amps and therefore uses less power. The client fixates on that and know looks for you to come up with 3 phase. George Remember one of the first rules of Electricity: You can NEVER do better than your original source Also well stated. JMO, Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Mar 2002
Posts: 360
Member
|
In the circles I run in, there are home machine shops. Phase converters all over theplace because most machine tools are built around 3 phase motors. Because they are smaller for the given power, and prob'ly the real reason, they are easy to reverse. This business owner might be in for a unit big enough that single phase power is a special order. but I doubt it. This is going to cost more in engineering and upkeep than it's worth. :two cents: now I'm too broke to pay attention TW
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
Be extremely cautious of the claimed capability of “Phase Converters.”
Hermetic-compressor manufacturers state that over 2% voltage unbalance is unacceptable, to the point of disqualifying warrantee replacement.
|
|
|
|
Joined: Dec 2003
Posts: 886
Member
|
...or essentially a single phase motor/three phase generator rolled into a single rotating machine (rotary phase converter). You can even use a plain ordinary three phase induction motor as a rotary phase converter; you power it from your single phase supply through two of the leads, do something mechanical to start it spinning (since a single phased 3 phase motor won't _start_), and once it is spinning you can draw the third leg from the motor terminal.
Something that has always bothered me about this- how do you get true three phase which is 120-120-120 degrees out of single phase which is 180-180 degrees unless you use a true motor generator? (Single phase motor coupled to a three phase generator.)
All rotary converters I have ever seen use the single phase hot legs and create a third phase from them. This works if a three phase motor loses a phase- it will generate the third. But the "input" is already two phases at 120-120 degrees.
There was recently a question from someone who was using a rotary converter that supplied 240 volts. He was using a buck transformer arrangement to buck it down to 208. He couldn't figure out why the voltage was not consistant on all three phases. I suggested it was because the phase difference was not 120-120-120 degrees as the transformers expected to see.
-Hal
|
|
|
|
Joined: Sep 2003
Posts: 650
Member
|
Something that has always bothered me about this- how do you get true three phase which is 120-120-120 degrees out of single phase which is 180-180 degrees unless you use a true motor generator? (Single phase motor coupled to a three phase generator.)
All rotary converters I have ever seen use the single phase hot legs and create a third phase from them. This works if a three phase motor loses a phase- it will generate the third. But the "input" is already two phases at 120-120 degrees.
There are three questions hidden here. 1) How do you get _any_ phase angle difference from the single phase machine? The answer is that you have stored energy in the mechanically moving rotor, just as you would in a true motor-generator. The single phase supply attached to one of the phase bands causes the rotor to move. The moving magnetized rotor interacts with the other phase bands in turn, and since the other phase bands are mechanically displaced, the voltage on those phase bands is displaced in time. 2) How do you get _exaxtly_ 120-120-120 with balanced voltage? Alas, you don't. You have three separate circuits which are _not_ the same. Current flows (and thus voltage drops) are different. The system will come close. If you use an ordinary three phase induction machine as your phase converter, the machine is designed with balanced coils, and _must_ produce unbalanced output. If you design the machine with unbalanced coils, then at a particular load condition it could produce balanced output. 3) If you have a three phase 120-120-120 supply, and one phase legs goes dead, what is the phase relation on the remaining two legs? The phase to _neutral_ phase angle remains 120 degrees. However for a motor without neutral connection, losing _one_ of the phase legs means that you have lost _two_ of your three phase supply circuits. What is left is a _single_ phase circuit, with 180 degree phase relation between its two supply terminals. For _any_ load connected between _two_ supply terminals, be they two hots or a hot and a neutral, or the hot and a tap on an autotransformer, the current flowing in from one supply terminal must be balanced by the current flowing out on the other supply terminal. -Jon
|
|
|
|
Joined: Oct 2000
Posts: 2,723 Likes: 1
Broom Pusher and Member
|
Tell the Client to use 2 or 3 separate 1Ø HVAC Packages, and forget the whole Phase Corn-Verter idea + 3Ø HVAC Package! Just venting my 2¢ Scott35