winnie: let you know this is a genral usage motor 7.5 hp @1780 rpm [ this came off from nameplate. thanks .
![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
Wowsers. Making that work would require a hefty receptacle...probably cheaper to install a 240 to 600V step up transformer, suitable (lower current) receptacle, and get a 600V motor (*grin*)
I stand by my contention that if this were a _listed_ _ampere rated_ _appliance_, that the ampere rating could be used to determine conductor size, disconnect rating, and OCPD. But given that this is a general purpose _motor_ with a _horsepower_ rating sitting on an appliance, the _horsepower_ rating is what holds sway.
In my mind, the only still open is weather the provision which permits the use of the ampere rating for the 'disconnect means' makes using the ampere rating okay for selecting a receptacle. Again, this would not apply to the present case, but I believe that it does apply to the 'big orange store' compressors.
Thanks all for a great discussion, and good news that you were able to educate your customer, marc.
-Jon