473
14
The grounding/Neutral system will not make any problems, many European places do still use a 230V system without a Neutral. Y transformer with 230V between the legs does have approx 130V from each leg to ground. Where you are (in Norway?) do you tend to see more 400Y/230 or 230Y/132 utility distribution systems?
Posts: 155 Likes: 4
Most of Norway has traditionally had a Y 230. but the center point has not been bonded to ground, so it has usually not been a neutral at all. New transformers for new buildings use the more common European system of 400/230V Y, quite similar to the US 480/277V system. It has been some regional differences, The Stavanger area used the 230/400 (Earlier 380/220) system, Arendal area used a grounded center on the 230y but no Neutral wire in the supply system.
1 member likes this:
tortuga |
Posts: 385 Likes: 1
Interesting question DSK and it was one that first brought me to this forum when I was seconded to the USA from 240V 50Hz land. I had a fair bit of 240V workshop equipment plus that very British of requirements a 240V kettle, all 3kW of it! The question I asked at the time (in the very early noughties) was can a 240V (NEMA6-20) be installed in a US kitchen?
A great deal of debate ensued including issues around GFCI which, as has been pointed out above, can be rather expensive. The final outcome was that yes I could as it was for a dedicated piece of equipment and that the code requirements for GFCI in the kitchen only applied to 120V circuits.
A search might find the original post but it has surpassed my ability to do so.
Posts: 10,055 Likes: 40
A search might find the original post but it has surpassed my ability to do so. It is true that 210.8 (A) still says (A) Dwelling Units. All 125-volt, single-phase, 15- and 20- ampere receptacles installed in the locations specified in 210.8(A)(1) through (10) shall have ground-fault circuit- interrupter protection for personnel.
I other than dwelling units your 6-15 would need GFCI protection in a kitchen. (B) Other Than Dwelling Units. All single-phase receptacles rated 150 volts to ground or less, 50 amperes or less and three- phase receptacles rated 150 volts to ground or less, 100 amperes or less installed in the following locations shall have ground-fault circuit-interrupter protection for personnel
Posts: 385 Likes: 1
[quote](A) Dwelling Units. All 125-volt, single-phase, 15- and 20- ampere receptacles installed in the locations specified in 210.8(A)(1) through (10) shall have ground-fault circuit- interrupter protection for personnel. It should be highlighted, through omission, as the 'Englishman's Clause'  Tea anyone ? ...
The tea kettle seems to be the only attractive appliance for 230-240v. Most things do quite well with 1440 watts max. Since we don't drink that much hot tea here, it hasn't been an issue. I cold brew my iced tea, no global warming involved at all
Posts: 7,413 Likes: 10
We have had a few residential, (high end) that have 30 amp, and 50 amp 240 volt receptacles in the kitchens or adjacent 'butler pantry. Rice cookers, and oh yes, the 'tea kettle' (mini boiler).
Design pro, and ECs installed GFI breakers; no argument from me.
I would not recommend using NEMA receptacles, as there is more possibility of the end users messing up the cords cutting and re capping all their appliances. I'm in the US of course and my knowledge of foreign methods is limited to what I've read in books and here online (and of course that which I have to imply when my jobs hand me equipment meant for use elsewhere and expect me to figure out wtf to do with it). That said I've seen many references to the number of different connectors available in European countries, and apparently it's not uncommon for the layperson to buy appliances and have to attach their own cord caps... Apparently that's just a normal thing most people are expected to be able to do.