0 members (),
174
guests, and
29
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
OP
Member
|
2020 seems to be requiring the dryer to be on a GFCI. It also seems to be saying if you have 240v receptacles in the garage for compressors, welders etc, they need to be GFCI.
Greg Fretwell
|
|
|
|
Joined: Mar 2004
Posts: 814
Member
|
2020 seems to be requiring the dryer to be on a GFCI. It also seems to be saying if you have 240v receptacles in the garage for compressors, welders etc, they need to be GFCI. I'm glad I'm retiring this year
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
OP
Member
|
The article in EC&M seems to be saying the objective is to put everything on a GFCI or an AFCI maybe both since some of the examples they use are already required to be AFCI. The reality is all they really need to do is redesign the AFCI breaker with 5ma GF protection instead of 30ma. I think the goal is to make the simple circuit breaker obsolete.
Greg Fretwell
|
1 member likes this:
David1 |
|
|
|
Joined: Dec 2002
Posts: 206
Member
|
I wouldn't fancy 5mA GF breakers. They'd be continually nuisance tripping due to current from capacitive filters, imperfect heating elements or minor dampness from condensation somewhere.
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
OP
Member
|
Welcome to our world The reality is the safety people have decided 30ma is well up into the freeze category. (where you can't let go) It will protect equipment but it is still too much current to reliably protect people.
Greg Fretwell
|
|
|
Posts: 32
Joined: June 2004
|
|
|
|
|