Meadow #219218 03/30/18 08:10 AM
Joined: Jun 2014
Posts: 145
Likes: 2
D
dsk Offline
Member
Things takes time, the building process is not finished yet, and the cable are still running trough the house. :-)

dsk

Meadow #219567 08/28/18 02:54 PM
Joined: Jun 2014
Posts: 145
Likes: 2
D
dsk Offline
Member
They has had proffesionals there now, and the cables are now propery put in the ground with the right kind of cable, and terminations.

Attached Images
2018-08-18 11.00.33.jpg
Last edited by dsk; 08/28/18 02:58 PM.
Meadow #220040 04/19/19 10:29 AM
Joined: Jun 2014
Posts: 145
Likes: 2
D
dsk Offline
Member
I am wondering how they will do it, but someone was telling me that they want to convert the area from 230V TT to 400/230 TNC-S

My guess will be a transformer with both voltages, and dirstibution of of the 400V system to new houses.


Meadow #220043 04/20/19 06:27 PM
Joined: Dec 2001
Posts: 2,498
T
Member
They could convert the existing buildings too, it'd take new cables and some inside work too. I guess a dual-voltage transformer wouldn't be enough for running both systems in parallel since the old setup requires a floating star point (IT) while the new one needs an earthed one (TN).

Meadow #220050 04/26/19 03:56 AM
Joined: Jun 2014
Posts: 145
Likes: 2
D
dsk Offline
Member
The old system is a TT system so it will probably be OK, In the neighborhood they even have a transformer with 2 separate secondary winding's too.

dsk

Meadow #220058 05/02/19 08:01 PM
Joined: Dec 2001
Posts: 2,498
T
Member
I suppose they could convert the older parts to 133/230 V TT if they're currently 133/230 IT with earthed local PE. That'd be the Belgian system, once common in quite a few European countries. They'd still need a transformer with separate secondaries I guess. If all existing supplies are single phase (i.e. only two out of the three phases are supplied, giving 230 V) they could replace the distribution and reconnect the existing buildings to 230 V line to neutral instead.

Meadow #220062 05/03/19 04:30 AM
Joined: Jun 2014
Posts: 145
Likes: 2
D
dsk Offline
Member
It is already 133/230 TT, so I guess that is the way they will do it.

dsk #220764 04/29/20 12:54 PM
Joined: Apr 2020
Posts: 9
W
New Member
Originally Posted by dsk
It is already 133/230 TT, so I guess that is the way they will do it.



138/240Y TN-S without the neutral distributed is an ideal system.

If I'm not mistaken 127/220Y is very common in South America.



Meadow #220819 05/27/20 11:43 AM
Joined: Apr 2020
Posts: 9
W
New Member
Here is an interesting PDF (yes I know its in Norwegian but can be translated). Stresses importance of RCDs in IT systems due to the lack of interconnected ground systems between buildings:


https://automasjonslab.files.wordpress.com/2018/11/jording.pdf