FPE in Germany pt.2

Uploaded for another forum thread
Horizontal Ad
4 Comments
Joined: Apr 2020
Posts: 9
W
New Member
Thank you for posting this. Looks like German FPE breaks have a magnetic trip coil not found in the US versions.

Joined: Oct 2000
Posts: 5,393
S
Member
Can you cite an example of mag trip coil for viewer reference please?

~S~

Joined: Apr 2020
Posts: 9
W
New Member
Here is an example inside an EU breaker (labelled as a solenoid):

https://www.engineersgarage.com/sit...ageupload/4214/Internal-Parts-of-MCB.jpg


Joined: Aug 2008
Posts: 62
A
andey Offline OP
Member
That is correct, Wateringress. The coil in my photo is on the left side, hidden under the sheet metal fin.

I'm not sure about the whole EU, but all breakers in Germany, since many decades, have these two working mechanisms. The bimetal strip to act time-delayed in overload condition, and the coil for instant trip in short circuit situations. There's different trip curves but the most common curve is "B" where the instant trip will start working at 3 to 5 times the nominal current.
With the most common breaker for regular outlets being B 16 Amp, the fault loop impedance must be low enough to have at very least 80 Amp flow in case of a short, to trigger the instant trip. This is also something the contractor needs to prove by measurement with a special meter.
A common value for the available short circuit current in a regular panel of a German appartment is around 300-2000 Amp. Depending on the distance to the transformer and wiring. So if the wire from the breaker to the outlet is not too long, and terminations are good, you easily make the 80 Amp plus some functional reserve.

Last edited by andey; 06/23/20 06:49 AM.

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Admin
Admin
NY, USA
Posts: 3,672
Joined: October 2000
Top Posters(30 Days)
Trumpy 5
davey 1
Popular Topics(Views)
552,376 Are you busy
427,040 Re: Forum
397,465 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5