#220378 12/09/19 01:46 PM
3 Images
Joined: Aug 2008
Posts: 62
A
andey Offline OP
Member
FPE in Germany pt.2

Uploaded for another forum thread
4 Comments
Joined: Apr 2020
Posts: 9
W
New Member
Thank you for posting this. Looks like German FPE breaks have a magnetic trip coil not found in the US versions.

Joined: Oct 2000
Posts: 5,392
S
Member
Can you cite an example of mag trip coil for viewer reference please?

~S~

Joined: Apr 2020
Posts: 9
W
New Member
Here is an example inside an EU breaker (labelled as a solenoid):

https://www.engineersgarage.com/sit...ageupload/4214/Internal-Parts-of-MCB.jpg


Joined: Aug 2008
Posts: 62
A
andey Offline OP
Member
That is correct, Wateringress. The coil in my photo is on the left side, hidden under the sheet metal fin.

I'm not sure about the whole EU, but all breakers in Germany, since many decades, have these two working mechanisms. The bimetal strip to act time-delayed in overload condition, and the coil for instant trip in short circuit situations. There's different trip curves but the most common curve is "B" where the instant trip will start working at 3 to 5 times the nominal current.
With the most common breaker for regular outlets being B 16 Amp, the fault loop impedance must be low enough to have at very least 80 Amp flow in case of a short, to trigger the instant trip. This is also something the contractor needs to prove by measurement with a special meter.
A common value for the available short circuit current in a regular panel of a German appartment is around 300-2000 Amp. Depending on the distance to the transformer and wiring. So if the wire from the breaker to the outlet is not too long, and terminations are good, you easily make the 80 Amp plus some functional reserve.

Last edited by andey; 06/23/20 06:49 AM.

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
BigB 9
Popular Topics(Views)
302,491 Are you busy
231,879 Re: Forum
216,505 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5