What's wrong here??

A few boo boo's in this 'ready for cut-in card' to POCO.

Name a few??
10 Comments
Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
I would start with the lack of bond bushings and the unbalanced phase conductors in the nipples.
I have seen guys who would call the metallic nipples there a parallel neutral too but I have never called that one.

Joined: Dec 2000
Posts: 4,291
Member

The sheet metal is likely to be hot enough to cook an egg, with the neutrals in a separate conduit from the hots.

(Are those grounding locknuts on those nipples?)

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
I suggested cooking a pop tart between the cabinets in another thread with this picture but we are on the same page.
I suppose they may have cut a slot between the holes to break the flux lines but I would want to see it.


Greg Fretwell
Joined: Mar 2015
Posts: 76
A
Member
Is it also that the neutrals seem to be bolted directly to the metal box thats a big no no in the UK but don't know about US/CANADA practice

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
This is a CT (metering)cabinet on the line side of the service disconnect so there is no real difference between neutral and ground.


Greg Fretwell
Joined: Apr 2002
Posts: 7,333
Likes: 7
Member
The real tight bend radius on 'c' (yellow) line side, stressed & bent the CT. POCO inspector was not a happy camper about that, after he recovered from a long fit of laughter.

After two (2) attempts, it finally passed inspection.



John
Joined: Apr 2002
Posts: 7,333
Likes: 7
Member
annemarie1:

BTW, the neutrals within the CT can be 'as pictured, IF the install is hot sequence. (CT before Main OCP). IF cold sequence (Main before CT) the neutral must be isolated from ground. (Floating). This is an occasional 'Fail' for some that are not well versed in CT installs.

(Sequence varies by POCOs)


Last edited by HotLine1; 02/02/17 04:36 PM.
Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
I have never seen a CT on the load side of the service disconnect because they usually want to seal the CT can and everything on the line side. The service disconnect, MBJ etc has to remain accessible. That may just be a local interpretation of "accessible" tho.


Greg Fretwell
Joined: May 2005
Posts: 984
Likes: 1
G
Member
Many Utilities put their CTs on the line side (to keep people from stealing power), but it can increase the risk to their own people...others have different priorities.


Ghost307
Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,601 Are you busy
231,932 Re: Forum
216,569 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5