What's wrong here??
#218083
01/27/17 12:45 AM
|
Joined: Apr 2002
Posts: 7,227
OP
Member
|
What's wrong here??
A few boo boo's in this 'ready for cut-in card' to POCO.
Name a few??
|
|
|
Re: What's wrong here??
[Re: HotLine1]
#218094
01/27/17 04:59 AM
|
Joined: Jul 2004
Posts: 9,557
Member
|
I would start with the lack of bond bushings and the unbalanced phase conductors in the nipples. I have seen guys who would call the metallic nipples there a parallel neutral too but I have never called that one.
|
|
|
Re: What's wrong here??
[Re: HotLine1]
#218147
01/31/17 01:31 AM
|
Joined: Dec 2000
Posts: 4,287
Member
|
The sheet metal is likely to be hot enough to cook an egg, with the neutrals in a separate conduit from the hots.
(Are those grounding locknuts on those nipples?)
|
|
|
Re: What's wrong here??
[Re: HotLine1]
#218149
01/31/17 02:22 AM
|
Joined: Jul 2004
Posts: 9,557
Member
|
I suggested cooking a pop tart between the cabinets in another thread with this picture but we are on the same page. I suppose they may have cut a slot between the holes to break the flux lines but I would want to see it.
Greg Fretwell
|
|
|
Re: What's wrong here??
[Re: HotLine1]
#218155
02/01/17 10:08 PM
|
Joined: Mar 2015
Posts: 76
Member
|
Is it also that the neutrals seem to be bolted directly to the metal box thats a big no no in the UK but don't know about US/CANADA practice
|
|
|
Re: What's wrong here??
[Re: HotLine1]
#218156
02/02/17 03:52 AM
|
Joined: Jul 2004
Posts: 9,557
Member
|
This is a CT (metering)cabinet on the line side of the service disconnect so there is no real difference between neutral and ground.
Greg Fretwell
|
|
|
Re: What's wrong here??
[Re: HotLine1]
#218159
02/02/17 04:32 PM
|
Joined: Apr 2002
Posts: 7,227
OP
Member
|
The real tight bend radius on 'c' (yellow) line side, stressed & bent the CT. POCO inspector was not a happy camper about that, after he recovered from a long fit of laughter.
After two (2) attempts, it finally passed inspection.
John
|
|
|
Re: What's wrong here??
[Re: HotLine1]
#218160
02/02/17 04:35 PM
|
Joined: Apr 2002
Posts: 7,227
OP
Member
|
annemarie1:
BTW, the neutrals within the CT can be 'as pictured, IF the install is hot sequence. (CT before Main OCP). IF cold sequence (Main before CT) the neutral must be isolated from ground. (Floating). This is an occasional 'Fail' for some that are not well versed in CT installs.
(Sequence varies by POCOs)
Last edited by HotLine1; 02/02/17 04:36 PM.
|
|
|
Re: What's wrong here??
[Re: HotLine1]
#218164
02/03/17 02:28 AM
|
Joined: Jul 2004
Posts: 9,557
Member
|
I have never seen a CT on the load side of the service disconnect because they usually want to seal the CT can and everything on the line side. The service disconnect, MBJ etc has to remain accessible. That may just be a local interpretation of "accessible" tho.
Greg Fretwell
|
|
|
Re: What's wrong here??
[Re: HotLine1]
#218166
02/03/17 10:58 AM
|
Joined: May 2005
Posts: 984
Member
|
Many Utilities put their CTs on the line side (to keep people from stealing power), but it can increase the risk to their own people...others have different priorities.
Ghost307
|
|
|
|
|