0 members (), 247 guests, and 14 robots.
#21794 02/11/03 08:10 AM
Turkey,
If it is installed outdoors, you can not install NM cable inside the EMT, it would have to be UF.
If a conduit is installed in a wet location, the interior of it is considered a wet location as well. NM cable is only suitable for normally dry locations per 334.10 (A)
BTW,
There are those who believe that NM cable installed in conduit is a violation of 334.40 which requires it to be secured within 12" of your boxes, etc. If the cable is in conduit, this requirement can not be met.
#21795 02/11/03 08:27 AM
Redsy, boxes do have interior clamps which would meet code.
Sparky, the conduit would be grounded provided the romex ground was connected to the box.
#21796 02/11/03 10:07 AM
Turkey,
Why would you run romex in emt. It seems to me to be much easier to run THWN in the conduit instead.
#21797 02/11/03 10:51 AM
I don't understand the concept of running romex in conduit!! That 10/3 romex, will hardly fit in ½" and will still be tight in 3/4", even in 3/4" you won't get 10/3 around more than 1 90 degree bend. Save yourself a lot of headache and use single conductors in the conduit. If it is in the middle of the run splice in correctly sized boxes at each end.
#21798 02/11/03 12:41 PM
10 ga. THWN would be a better choice, and cheaper too.
gramps
#21799 02/11/03 12:53 PM
tsolanto,
I'm not sure the conduit can be connected to the box if it is the type of box that has NM cable clamps?
BTW,
I am not opposed to the practice of using a section of EMT for protecting drops of NM cable to outlet boxes, in a basement, for example.
I know of at least one authority who considers it a violation. My opinion is that, with a proper transition fitting, the intent of the above mentioned article is satisfied.
Still thumbs down on wet locations, though.
[This message has been edited by Redsy (edited 02-11-2003).]
#21800 02/11/03 01:56 PM
This is the very type of thing that caused so many problems in getting a workable code passed. I believe that Mr. M, a board member, said it all when he insisted that "common sense" prevail. I have minimal amounts of romex in EMT as well as PVC. As long as the EMT has watertight fittings and boxes there is no valid reason to exclude.
Many of the farms in the county have EMT w/romex, most in WP raceways. They are used for grain dryers, farrow houses, butchering houses, etc and as some are under the county health dept full inspections as to safety are performed.
Rowdy
#21801 02/12/03 10:05 PM
As has been noted romex is only allowed in a normally dry location. No matter what type of conduit usad in a wet or damp location especally outside you will get some condensation in it. How much depends on mother nature's weather in your area. Outside is a violation. Inside may not be if you can make the appropate transitions between wiring methods.
ed
#21802 02/13/03 08:17 AM
Here in Long Island romex was allowed for many years to be installed in conduit outside. It lasted indefinetly.... I have never encountered a problem caused by this practice. However in the last year or so the AHJ's are now violating this practice for the reasons described in this post.
Don't agree with it...Gota live with it...