Meadow #214517 12/17/14 10:24 PM
Joined: Sep 2011
Posts: 66
M
Meadow Offline OP
Member
DSK, I think you will like this very interesting:

http://assets.fluke.com/manuals/1654bit_iseng0000.pdf

Horizontal Ad
Meadow #214523 12/18/14 07:44 AM
Joined: Jun 2014
Posts: 152
Likes: 4
D
dsk Offline
Member
Great link, thank you.

Why IT? When I asked som 30 years ago, they claimed it to be safer. We should modernize a system from 1940 (IT) and the supplier would change the transformer at the same time, we offered to pay the extra cost to change to 400V TN-S or TN-C-S
but they refused "of safety reasons".

Blessed are the meek,
For they shall inherit the earth. !

dsk #214534 12/19/14 06:32 AM
Joined: Sep 2011
Posts: 66
M
Meadow Offline OP
Member
Originally Posted by dsk
Great link, thank you.

Why IT? When I asked som 30 years ago, they claimed it to be safer. We should modernize a system from 1940 (IT) and the supplier would change the transformer at the same time, we offered to pay the extra cost to change to 400V TN-S or TN-C-S
but they refused "of safety reasons".

Blessed are the meek,
For they shall inherit the earth. !


Welcome laugh



I agree it safer, personally short the nullpunkt sikring ( http://www.el-tjeneste.no/files/Brosjyre-Nullpunktsikring.pdf ) and run a PE from the transformer N to all homes and you have the safest system.

Shame some are taking TN-C-S frown


Meadow #214741 01/18/15 03:53 PM
Joined: Jun 2014
Posts: 152
Likes: 4
D
dsk Offline
Member
Some pictures of new vs. old transformer in the Lillehammer area. [Linked Image from img.photobucket.com]
[Linked Image from img.photobucket.com]
[Linked Image from img.photobucket.com]

Last edited by dsk; 01/18/15 04:04 PM.
Meadow #214863 02/01/15 04:36 AM
Joined: Sep 2011
Posts: 66
M
Meadow Offline OP
Member
Thank you! laugh laugh laugh

What connection are the transformers?

Are those boxes on the LV fuses?


Meadow #214864 02/01/15 06:52 AM
Joined: Jun 2014
Posts: 152
Likes: 4
D
dsk Offline
Member
Right, And a nice lady at eidsivaenergi.no will send us data about the transformers. This looks to turn out well for the forum.

dsk

Meadow #214879 02/02/15 01:51 AM
Joined: Jul 2002
Posts: 8,450
Likes: 4
Member
Originally Posted by Meadow

What connection are the transformers?
Are those boxes on the LV fuses?


Generally, the primary side (HV) will be Delta connected, the Secondary side (LV) will be Star connected.
By the looks of things, the two black boxes on the left pole are triple pole LV fuse-switches, when you open them up, it cuts power to the load side of the fuses.
The HV side is fused by DDO type expulsion fuses seen on that intermediate cross-arm as part of the vertical air-break switch.

Horizontal Ad
Meadow #214891 02/04/15 04:22 PM
Joined: Sep 2011
Posts: 66
M
Meadow Offline OP
Member
Thanks! Id be very interested in the windings and data plate.

If you zoom on this picture: http://commons.wikimedia.org/wiki/File:Three-phase_distribution_transformator_IMG_8086_Hurum_Norway_23kV_240V.JPG

The data plate says Yyn0.

Which would come out as ungrounded wye primary with a wye secondary neutral brought out.

Now that I think about it, if the primary is wound wye, wouldn't it be so it can be solidly grounded? What would the IEC designation be for that?

I see what looks like a forth ground/neutral wire on the MV, so it would make sense then.

A primary grounded wye has the advantage of being resistant to ferroresonance, which Id imagine is more of a concern at 22kv and a long run.

Unless the primary is ungrounded wye? If ungrounded, than why wye and not delta? An ungrounded wye with a shorted secondary nullpunkt and one 230 volt phase faulted would make for some very interesting conditions.

Very interesting.

Last edited by Meadow; 02/04/15 04:28 PM.
Meadow #214911 02/06/15 03:30 PM
Joined: Jun 2014
Posts: 152
Likes: 4
D
dsk Offline
Member
It has been extremely silent from eidsivaenergi.no so far.

dsk

Meadow #214912 02/06/15 05:42 PM
Joined: Sep 2011
Posts: 66
M
Meadow Offline OP
Member
Its ok, things take time smile

Page 9 of 14 1 2 7 8 9 10 11 13 14

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,450
Joined: July 2002
Top Posters(30 Days)
Trumpy 5
dsk 1
davey 1
Popular Topics(Views)
552,870 Are you busy
427,466 Re: Forum
397,967 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5